Applying the 1.20 correction factor is only used at the design stage when we use the calculated mv/a/m which are given at 20 degrees and we wish to correct to 70 degrees.Hi, Could anyone check my calculation please.
Protective device 60A 1361
E.S = TN-C-S
Cable 16mm T & E
CPC 6.0mm
Zdb = 0.43ohms
Multiplier temp 1.20
0.43 x 1.20 = 0.52ohms
230/0.52 = 442A
SR 442 squared x 2secs/115 = 5.43mm
Cheers
If you have took a measured zs and got 0.43 for the sub main circuit then use that value.Hi, the supply goes from the intake to a switched fuse, then to the consumer unit. Ze is 0.35. The multiplier is for the rising temperature of the conductor under fault conditions.
Cheers
The basic equation is just I2t square root/k.When using the adiabatic in cable design calculations, I don't use any temperature correction, but i'm almost certain when calculating if the cpc is large enough, temperature rise under fault conditions must be taken into consideration. But im probably wrong
The 1.6s is what I estimated from the graph at 442A.Thanks richard, Ian.
I used the 2 secs as that was the closest in the curve charts. is 1.6s the actual disconnection at 442A
So temperature correction is not to be used.
Where have you got the 0.65s from?
Cheers much appreciated