Hi, Could anyone check my calculation please.
Protective device 60A 1361
E.S = TN-C-S
Cable 16mm T & E
CPC 6.0mm
Zdb = 0.43ohms
Multiplier temp 1.20
0.43 x 1.20 = 0.52ohms
230/0.52 = 442A
SR 442 squared x 2secs/115 = 5.43mm

Cheers
 
Hi, Could anyone check my calculation please.
Protective device 60A 1361
E.S = TN-C-S
Cable 16mm T & E
CPC 6.0mm
Zdb = 0.43ohms
Multiplier temp 1.20
0.43 x 1.20 = 0.52ohms
230/0.52 = 442A
SR 442 squared x 2secs/115 = 5.43mm

Cheers
Applying the 1.20 correction factor is only used at the design stage when we use the calculated mv/a/m which are given at 20 degrees and we wish to correct to 70 degrees.
Is it zdb or the actual ze of 0.43 ohms?
 
Hi, the supply goes from the intake to a switched fuse, then to the consumer unit. Ze is 0.35. The multiplier is for the rising temperature of the conductor under fault conditions.
Cheers
 
Hi, the supply goes from the intake to a switched fuse, then to the consumer unit. Ze is 0.35. The multiplier is for the rising temperature of the conductor under fault conditions.
Cheers
If you have took a measured zs and got 0.43 for the sub main circuit then use that value.
Remember we are testing at site temperatures which is why we apply the 80% rule of thumb to the given max zs value of bs7671 when testing.
There is no need to apply the 1.20 value as that’s why we apply the 80% value.
As long as when it’s measured the value is equal to or less than the the 80% value of the 100% bs7671 value then You are good.
 
When using the adiabatic in cable design calculations, I don't use any temperature correction, but i'm almost certain when calculating if the cpc is large enough, temperature rise under fault conditions must be taken into consideration. But im probably wrong
 
When using the adiabatic in cable design calculations, I don't use any temperature correction, but i'm almost certain when calculating if the cpc is large enough, temperature rise under fault conditions must be taken into consideration. But im probably wrong
The basic equation is just I2t square root/k.
K is the value of the conductor at an assumed operating temp such as a single cpc not bunched operating at max temp of 70 degrees, k is given as 143
No correction factors are applied.
 
Fault current would be higher at lower temperatures as the resistance will decrease so the shortest disconnection time would be starting at 20°C, ambient temperature, a longer disconnection time because of increased resistance (at 70°C) may stress a conductor more due to the increased time it has to carry the fault current.
Generally a measured PEFC is what I might use, but the k values given in the tables show the assumed initial temperature, which is 70°C for a conductor incorporated in a cable, as in your case, so the fault current should be that experienced at 70°C.

However with a fault current of 442A I would give a disconnection time of 1.6s rather than 2s for a 60A BS1361.
(With a fault current of (230/0.43)=535A I would apply a disconnection time of 0.65s for a 60A BS1361.)

As the cable is the cpc of a twin and earth the k value is 115 as you have stated.
Using the figures you have used the calculation is mathematically correct.
Using a disconnection time of 1.6s would calculate to a minimum cpc size of 4.86 mm².
Using a disconnection time of 0.65s and current of 535A would calculate to 3.75 mm².

In all cases the cpc is large enough to carry the fault current.
 
As for temperature rise if your concerned,you just need to confirm that t=K2S2/I2
The time t , in which a given fault current will raise the live conductors from the highest permissible operating temperature in normal duty to the limiting temperature before damage to the conductors and surrounding insulation occurs
 
Thanks richard, Ian.
I used the 2 secs as that was the closest in the curve charts. is 1.6s the actual disconnection at 442A
So temperature correction is not to be used.
Where have you got the 0.65s from?

Cheers much appreciated
 
Thanks richard, Ian.
I used the 2 secs as that was the closest in the curve charts. is 1.6s the actual disconnection at 442A
So temperature correction is not to be used.
Where have you got the 0.65s from?

Cheers much appreciated
The 1.6s is what I estimated from the graph at 442A.

With a fault current of 535 A as calculated from a Zdb of 0.43 Ω and a design voltage of 230 V, I estimate that the disconnection time on the graph would be 0.65 s.
 
If an RCD is being used for fault protection then the adiabatic equation would not apply to an earth fault as the requirement is then (for a TT) that Ra * Idn <50V.

However you could consider that the RCD disconnection time at say 442 A (perhaps using the 5 x idn value as measurement would be dangerous above this) could be used to ensure that the cpc was not damaged. This is just my thoughts not a recommendation.
 
You could use 0.04 as your max disconnection time as required by the standards, if the fault current exceeds 5xId. If the cable had a 1.5mm CPC and the value of K was 115.

115 squared= 13225

1.5 squared= 2.25

13225 x 2.25=29756.25 A2

Zs=0.43 ohms

230V/0.43=535A

535 squared=286225 A2

286225 x 0.04=11499 A2s

Therefore handling the thermal and mechanical stresses of the earth fault current during disconnection.
 
Hi Lee, that doesn’t make sense at all to me. I was told similar to what Richard burns has said. Rcd in circuit, line & neutral loop is all I should be concerned about. An electrician went through the Adiabatic with me with a 30ma Rcd in circuit, which he said was pointless, he used the pefc at the far end of the circuit. Time used was 300ms.
Cheers
 

Reply to Help with Adiabatic equation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi was wondering if im doing this right. The question in: Determine for a chosen circuit "the minimum possible csa of cpc which will satisfy the...
Replies
26
Views
4K
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Now I know this has probably been covered a few times but I'm struggling to come to terms with my own calculations. I would appreciate it if...
Replies
9
Views
5K
The Ghost
T
R
Evening all, I have a question regarding calculation of CPC on a 16mm T+E and wondered if you could help at all. I have done a board change and...
Replies
4
Views
2K
rattlehead85
R
Can somebody have a look at this and tell me which tree I'm barking up? Using the Adiabatic equation to determine the required size of main...
Replies
36
Views
17K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock