Hi,
just wondered what your thoughts are on this,
3 bed town house
Whole house ring final, mixture of 2.5 / 1.0 & 2.5 / 1.5 twin and earth cables,
End to ends = 0.78, 0.78, 1.6. R1r2 = 0.61 (spur).
ZS = 0.66!
BS7671 recommends a max of 100 square meters which using 2.5/1.5 = an r1r2 of 0.48.
Thus the readings appear that the circuit is over 100 square meters, as the max end to ends of line and neutral should be 0.72!
the zs is within the max for b32!
would you code 3 this or simply ignore it , as it is not unsafe, am I being too cautious?