I'm in the process of re wiring a kitchen, the customer has gone with a Smeg Range cooker with a nominal rating of 19.5kw, the circuit is all in, that doesn't worry me.

However the DNO has been out to renew the service head as it was in a poor state, in doing this they have downgraded the cut out to an 80amp/16mm tails.

The max demand is roughly 50amps currently, but I feel once the Range cooker is up and running the max demand is going to be very close to the 80amps.

Would you reccomend to customer to have DNO back to upgrade tails/cut out? I would feel more comfortable knowing there is a 100a/25mm tails incase Mary berry ever pops in to show them how it works..

Any advice is greatly appreciated :)
 
A cooker may have a maximum load of 19.5 kW according to the manufacturer, but if it ever pulled over 30 amps I would be very surprised
 
Diversity applied to cooker as you say is roughly 30 amps.

There are 2 ring circuits, 2 lighting, 16a radial and an immersion heater.

No electric shower, oil heating and no other big loads.

I may we'll be being over cautious here, after doing a walk around and applying diversity based on light points/socket outlets and immersion at 100%.
 
Is this an ordinary domestic kitchen? Who the hell would need a cooker that pulls nearly 85 Amps?? If I were you I would forget about exceeding the maximum load, what cable/OCPD have you put it on? How do you mean the DNO downgraded the tails?
 
Yes, ordinary domestic kitchen, it's ridiculous. I am going to try and explain to them tomorrow morning that in the nicest possible way, it's ridiculous.

I've gone for 10mm/45a or maybe 50a. Ref method C.

The tails from head to meter are now 16mm, I'm sure when I originally looked at the job they were 25mm, however I cannot be 100%.
 
I just looked at their web site and found a 19.5 KW with a listing specifying a 45 amp cooker switch
Even putting any diversity for this to one side and going with it drawing an unlikely 40 ish amp
It leaves you with a constant 40 amp to play with for the rest of the household loads,there appears to be a adequate supply from what appears to be a very ordinary demand
 
I just looked at their web site and found a 19.5 KW with a listing specifying a 45 amp cooker switch
Even putting any diversity for this to one side and going with it drawing an unlikely 40 ish amp
It leaves you with a constant 40 amp to play with for the rest of the household loads,there appears to be a adequate supply from what appears to be a very ordinary demand

Thanks, I will leave as is then. :)
 

Reply to Help with Range cooker.. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
967
Hi all, Just doing a newbuild where the DB will be about 8m from the cut out/meter box. 25mm tails run in conduit on the surface of the outside...
Replies
10
Views
2K
Hi, Before I begin my tale of woe, I have my tin hat ready! I'm retired from the trade, I started out just as the 16th came in and had a rather...
Replies
35
Views
4K
  • Locked
Hi, we need some advice on our scenario with regards to our rewire plan. I will get this out of the way first... We are planning to put the house...
Replies
24
Views
5K
hi This is just a starter because I haven't done any measurements yet (I was a guest there) and what I can do will be restricted as this has never...
Replies
10
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock