801
if you can help me along on the tick sheet cheers..

these are the faults i found today..


1.Cable duct not sealed C3

2. unterminated sy cable laying on floor (not live) C3

3. Rcd for additional protection not tripping in required times C2

4 no discrimination between protective devices C3

5. unterminated cable laying inside panel C3


Q. Does there need to be specific labelling for alternative supply? no fixed generator but has arrangement
 
1 what safety improvement are you recommending?
2 what safety improvement are you recommending?
3 yes it is potentially dangerous
4 needs more information,
5 what safety improvement are you recommending?




Sent from my iPad using Tapatalk
 
1.Cable duct not sealed C3
If the duct is required to be sealed then what is it sealing against, if the cable in the duct is not suitable for say water ingress and the duct cannot drain the water then this would give rise to danger. If the duct is not sealed and is in a dry area and the cable does not need protection of the insulation then this would be OK.


2. unterminated sy cable laying on floor (not live) C3
A piece of cable lying on the floor maybe a trip hazard but hardly comes under BS7671.

3. Rcd for additional protection not tripping in required times C2
Assuming the RCD was tested with all loads disconnected then yes.

4 no discrimination between protective devices C3
Does the lack of discrimination cause inconvenience or danger if not then this is not a problem, if it does affect the safety of the installation then the level of danger presented would narrow down the coding.

5. unterminated cable laying inside panel C3
This is poor practice; is the cable live or dead? if live and the panel cannot be opened without the use of a tool then C2, if the panel can be opened then C1. If dead then a comment.

If there is no alternative supply present at the time of inspection then the point is moot as there is no alternative supply for which the arrangement need to be in place.
 
1.
Cable duct not sealed C3

If the duct is required to be sealed then what is it sealing against, if the cable in the duct is not suitable for say water ingress and the duct cannot drain the water then this would give rise to danger. If the duct is not sealed and is in a dry area and the cable does not need protection of the insulation then this would be OK.
Reg. 527.2

2. unterminated sy cable laying on floor (not live) C3
A piece of cable lying on the floor maybe a trip hazard but hardly comes under BS7671.
Reg. 526.5


3. Rcd for additional protection not tripping in required times C2
Assuming the RCD was tested with all loads disconnected then yes.
Reg. 415.1.1

4 no discrimination between protective devices C3
Does the lack of discrimination cause inconvenience or danger if not then this is not a problem, if it does affect the safety of the installation then the level of danger presented would narrow down the coding.

as supplying water pumps and I'd say should be addressed

5. unterminated cable laying inside panel C3
This is poor practice; is the cable live or dead? if live and the panel cannot be opened without the use of a tool then C2, if the panel can be opened then C1. If dead then a comment.
Reg. 526.5

If there is no alternative supply present at the time of inspection then the point is moot as there is no alternative supply for which the arrangement need to be in place.



???????
 
1 OK no fire sealing where required C2
2 That regulation is hardly relevant for a dead cable
3 as before
4 down to the inspector on the ground
5 again is it live or dead?

If the alternative supply is intended to be used on a regular basis then it would be advisable to have the prescribed notices in place, but at the time of inspection there is no alternative supply so the notices are not required, definitely one for a comment to ensure that if the arrangement is used at any time then the required notices should be put in place in all the relevant locations.
 

Reply to help with schedule of inspections in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
My father In law is selling his property and had a EICR done recently requested by the buyers. I thought the report was not the best quality with...
Replies
23
Views
3K
I wonder if any electricians can offer some advice? I feel that I may be getting taken for a ride. I rent out a 2 bedroom flat built in 2005 that...
Replies
53
Views
6K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock