Code 3......it complies with the BGB in all aspects other than the recommended max of 200 ohms.....and assuming the RCD(s) operate within spec disconnection times are met.
No doubt there will be cries of anguish from some.....but the sole purpose of an EICR is to highlight deviations from BS7671,it is not permitted to bring personal preferences into coding. A code3 is nevertherless recommending improvement,and this could be explained more fully in the report summary.
 
Personally, I'd also code it 3, with a note in the comments box though looking at GN3 (new version) and the BGB I can't see any reference to a 'recommended max' of 200 ohms, only that values over 200 ohms may not be stable
 
I agree with the above.
In a TT with all circuits protected by 30mA RCD(s) then the impedance of the earth path could be as low as 1666ohms.

HOWEVER

400ohms is very low. Maybe its not in earth but sitting in a pit filled with hard core?
I would make it a Code 2 and recommend you bang in a new earth rod.
 
I agree with the above.
In a TT with all circuits protected by 30mA RCD(s) then the impedance of the earth path could be as low as 1666ohms.

Only while the RCD is working correctly!! lol!!

Agree with wirepuller in this instance, as this is conducting an official EICR to the current wiring regulations/BS7671.

...Not that i particularly agree with this section of them!! lol!!
 
Personally, I'd also code it 3, with a note in the comments box though looking at GN3 (new version) and the BGB I can't see any reference to a 'recommended max' of 200 ohms, only that values over 200 ohms may not be stable

I take your point...I've always considered this to be a roundabout way of recommending a max of 200ohms.....but you are correct,it's depends on your interpretation.
 
its in earth, down in cornwall on top of a big granite hill, I think it may take more than one rod to get it down much. PME is available in the area now so will recommend a phone call to the dno.
 

Reply to High Ze coding on new EICR in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock