- Reaction score
- 13
Still trying to get to grips with new EICR coding - got 400 ohms on earth rod all protected by 30mA rcd. What would you code this as under the new EICR?
Discuss High Ze coding on new EICR in the Electrical Forum area at ElectriciansForums.net
I agree with the above.
In a TT with all circuits protected by 30mA RCD(s) then the impedance of the earth path could be as low as 1666ohms.
Personally, I'd also code it 3, with a note in the comments box though looking at GN3 (new version) and the BGB I can't see any reference to a 'recommended max' of 200 ohms, only that values over 200 ohms may not be stable
Reply to High Ze coding on new EICR in the Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.