phawk
Can somebody help me please?
I'm just finishing a rewire, and I've installed a GF radial cicuit in a large domestic property and am in the process of testing it. It's a new radial circuit, 2.5 T&E, 13 sockets, 20A type B breaker on an RCD protected board. My R1&R2 = 1.40 and Ze = 0.20, so my calculated Zs should = 1.60 or just under (just within maz Zs).
The problem I have is that my Megger is giving me a Zs of 2.33 which is way over the max permitted of 1.85. It's even just over the 2.32 max permitted Zs of a 16A breaker which rules out dropping the breaker size.
As I am using this installation as my NAPIT assessment it needs to be spot on, so I really need to know why my meter is reading so high! I know I can note a calculated value of Zs, but if the assessor asks me to measure the Zs it will just be a flat fail.
I have been told it could be the impedance of the RCD, but I have also been told that Meggers are notorious for giving high Zs readings. Can anybody shed any light on this?
Points to note:
I don't have access to another tester to compare against.
My Megger has just been calibrated.
There are no loads in the circuit.
All connections are tight (R1+R2 = 1.41, R1+Rn = 1.40, R2+Rn = 1.14).
Thanks!
I'm just finishing a rewire, and I've installed a GF radial cicuit in a large domestic property and am in the process of testing it. It's a new radial circuit, 2.5 T&E, 13 sockets, 20A type B breaker on an RCD protected board. My R1&R2 = 1.40 and Ze = 0.20, so my calculated Zs should = 1.60 or just under (just within maz Zs).
The problem I have is that my Megger is giving me a Zs of 2.33 which is way over the max permitted of 1.85. It's even just over the 2.32 max permitted Zs of a 16A breaker which rules out dropping the breaker size.
As I am using this installation as my NAPIT assessment it needs to be spot on, so I really need to know why my meter is reading so high! I know I can note a calculated value of Zs, but if the assessor asks me to measure the Zs it will just be a flat fail.
I have been told it could be the impedance of the RCD, but I have also been told that Meggers are notorious for giving high Zs readings. Can anybody shed any light on this?
Points to note:
I don't have access to another tester to compare against.
My Megger has just been calibrated.
There are no loads in the circuit.
All connections are tight (R1+R2 = 1.41, R1+Rn = 1.40, R2+Rn = 1.14).
Thanks!