  1. Gavin John Hyde
    Offline

    Gavin John Hyde Regular EF Member

    Location:
    Somerset
    You aren't likely to see one of these everyday of the week but it is quite an interesting video i just saw, We are childminding tonight and my nephew is on a how its made binge on the youtube app on the tv... Didnt realise they had a firing pin in them mind!
     
    • Like Like x 3
    • Agree Agree x 1
  2. UKMeterman
    Offline

    UKMeterman Electrician's Arms

    These are HV fuses for fitting into 11KV ring main units.
     
    • Informative Informative x 1
  3. sparkdog
    Offline

    sparkdog sparkdog Electrician's Arms

    Location:
    Sunny Sussex
    Business Name:
    C MacRae Electrical
    Be a struggle getting that into a 13A plug.
     
    • Like Like x 1
    • Funny Funny x 1
  4. freddo
    Offline

    freddo Regular EF Member

    Location:
    Devon
    I have a similar one of those in my kitchen, it's not fitted with a striker. 63A 12KV. It's much heavier than it looks.
    upload_2017-12-8_0-8-53.jpeg
     
  5. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    All that would take,is a farmer,with a 240V compressor,a tractor with a flat tyre,and one blown standard fuse....and in it would go ;)
     
    • Like Like x 1
  6. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    All that would take,is a farmer,with a 240V compressor,a tractor with a flat tyre,and one blown standard fuse....and in it would go ;)
     
  7. I2C
    Offline

    I2C Electrician

    Location:
    East Sussex
    Agree with previous comments, these are for use with HV (High-Voltage).

    Why do they contain an explosive-charge?
    Put simply, high-voltages can jump through the air (like a police taser for example) and higher-voltages will jump considerably further than lower-voltages; the result is referred to as an 'arc / arcing'.

    The problem is that arcing creates very-high temperatures, especially in the area that the arc starts & finishes, which can easily melt metal (basically how welding works). The heat is therefore perfectly capable of damaging electrical conductors during disconnection, and must be avoided.

    With this said, explosive-disconnection-fuses are made for use in HV conductors and designed to detonate a small charge during fault-conditions, causing the conductors to separate very-quickly in order to prevent damaging-arcs.
     
  8. I2C
    Offline

    I2C Electrician

    Location:
    East Sussex
    This is a three-phase fuse which is installed on each of the individual phases. It's imperative that all phases simultaneously disconnect, opposed to a singular phase. The "firing-pin" is used to trigger the disconnection of the other phases during a fault to ensure safety.
     
    • Informative Informative x 2
    • Like Like x 1
    • Agree Agree x 1
  9. 1Justin
    Offline

    1Justin Electrician's Arms

    Location:
    Surrey
    Business Name:
    Circitas Ltd
    Likewise.. And I had no idea they would be wound on a spiral like that either. I can guess that compared to a straight element ( which I'd have expected), the spiral adds length so presumably reduces the relative heat-loss conducted out the ends in the event of a small overload.
     
  10. UKMeterman
    Offline

    UKMeterman Electrician's Arms

    Yes the firing pin hits the trip trigger for the contacts in the ring main unit so the other phases are also disconnected.
     
  11. Percyprod
    Offline

    Percyprod Regular EF Member

    Location:
    Cumbria
    It will only be about 25 amp
     
Loading...