Hi People,

Looked at a job today which requires adjustments to the CU and noticed there is 16mm from CU to MET which is cool, 10mm from MET to Gas main incoming, and bonding between all pipes coming in and out of the boiler linked off the GAS main bonding.

When I pointed out that there should be a 10mm to the mains water incoming the customer informed me that there was not one fitted as the incoming pipe is plastic, and most of the fittings in the house were a mixture of plastic and copper, so would be no use as an earth bond.

I could see his point, but where do we stand on such a situation?

Pip
 
just had a quick look at that pdf. it's 16th, out of date.

that was brought up last time we used it, but until something more resent is brought up..?...?...?

The reg I quoted is to date, and informs us that PVC supplied services with metallic framework downstream can be subject to bonding.
 
I thank you very much, it has been very enlightening, after I put up the post, I did look closer on the site and yes I can see why you are getting your De Ja vu, the question has been asked a few times recently, with some conflicting answers, which what you expect on such a subject

Again many thanks Pip
 
A plastic incoming service cannot, by definition, be an extraneous conductive part, ie. a part that is liable to introduce an earth potential or any other potential into an installation. Therefore main equipotential bonding is not required.

There is a standard test, described in GN8, to confirm whether an incoming service is or is not an extraneous conductive part. Using a high-reading ohm-meter, resistance is measured between the part and the MET of the installation. If above 56K Ohm it is not an extraneous conductive part.
 
but still not resolved in my opinion, sitemanager insists its not fitted, qs insists that a bond is made to wherever the incoming plastic turns to copper (wherever that may be), niceic are supposedly going to get back on this one, as stated earlier i would always bond at the first available place but it would be nice to get a definitive answer on this one.
 
but still not resolved in my opinion, sitemanager insists its not fitted, qs insists that a bond is made to wherever the incoming plastic turns to copper (wherever that may be), niceic are supposedly going to get back on this one, as stated earlier i would always bond at the first available place but it would be nice to get a definitive answer on this one.

When you say wherever the plastic changes to copper, are you talking about say 1 metre of copper, 8 metres of plastic, another metre of copper etc?
 
no mate copper incoming direct to stop tab then plastic in bathroom, goes underground and reappears near to combi which is the next closest place to put the bond.

one next door has copper intake then about 2 metres plastic returning to copper in same room, so a clamp can go on to the coper near the stop tap.

interested in your views on this as i still think a bond should be put in wherever the first point is that you can fit one. Everyone seems to have a diffent opinion.
 
A plastic incoming service cannot, by definition, be an extraneous conductive part, ie. a part that is liable to introduce an earth potential or any other potential into an installation. Therefore main equipotential bonding is not required.

There is a standard test, described in GN8, to confirm whether an incoming service is or is not an extraneous conductive part. Using a high-reading ohm-meter, resistance is measured between the part and the MET of the installation. If above 56K Ohm it is not an extraneous conductive part.


Hi where do you get that value from? The figure of 22KΩ sticks in my mind but tbh i can't remember off hand where i saw that.
 
When I spoke to one of the niceic's long standing engineer inspectors, he said you don't bond plastic water incomers, but if you want to do it, then don't bother asking me in the first instance.

He was the same person who said he does not agree with own technical team of technician's who say the existing bonding clamps attached to a lead incomer are unsuitable.

Therefore imo the niciec inspectors appear to interpret BS7671 differently from their own technical team, but they always say your the one signing the sheet. So I would do what I was happy with, no matter what I'm told by others.

And will never be told how to carry out my job by a QS or Site Agent and many other non Electrical trade person. You have a Duty of Care, that's where it Stops.
 
thata a good point so my view stands a main bond will be fitted at first available point (wherever that may be)

Fit the bond, your the electrician and you have a duty of care, and your name will go on the sheet in the one and only box of: designer, installer and tester.

I never do what I'm told to do if I'm not comfortable with it, end of.

Ive just gone on a job, ripping out 25mm bonding cables and running in new 50mm ones, I'm not sure there needed, but I'm not signing any sheets.
 
Last edited by a moderator:

Reply to How can you Earth Bond plastic incoming mains water pipe? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock