Ive got my am2 resit tommorow for my live testing and I ran out of time and failed as well as I carried out the ze test on 2 lead high thus tripping the rcd.
So now I know for next time to complete this on a 3 lead LOW test and measure ze with earth disconnected etc.. then connect main earth back after the test.
But how would you measure pefc and pscc on the three phase db.
The plan I had was for PEFC:-
Set the megger mft1740 to L-PE on 3 low test and croc on to the main earth first, then probe on the Neutral then the phase.
So I would do :- L1- N- E
L2- N -E
L3 -N-E
Note down the highest value for PEFC.
Then same connections set the tester to L-L/L-N to measure PSCC
Same test points again
L1-N-E
L2-N-E
L3-N-E
Note down the highest value as PSCC.
If meter can measure phase to phase then do the tests. But, if not simply take the highest value and times by 2 or more accurately 1.732.
Then record this value as PFC.
Is this right or should I be doing 2 lead low test, but wont this trip the rcd? I have in my mind to do 3 lead low test to not cause any imbalance in the rcd.
Cheers!
So now I know for next time to complete this on a 3 lead LOW test and measure ze with earth disconnected etc.. then connect main earth back after the test.
But how would you measure pefc and pscc on the three phase db.
The plan I had was for PEFC:-
Set the megger mft1740 to L-PE on 3 low test and croc on to the main earth first, then probe on the Neutral then the phase.
So I would do :- L1- N- E
L2- N -E
L3 -N-E
Note down the highest value for PEFC.
Then same connections set the tester to L-L/L-N to measure PSCC
Same test points again
L1-N-E
L2-N-E
L3-N-E
Note down the highest value as PSCC.
If meter can measure phase to phase then do the tests. But, if not simply take the highest value and times by 2 or more accurately 1.732.
Then record this value as PFC.
Is this right or should I be doing 2 lead low test, but wont this trip the rcd? I have in my mind to do 3 lead low test to not cause any imbalance in the rcd.
Cheers!