Hello all I'm doing a Job in France for my company where we are installing SWA for power to our own control panels
The issue is the DB is a new modular Schneider panel with removable sides all busbars switchgear etc is at the front and the access is really limited it's bolted to the floor and has large singles already installed in the top for the supply and therefore can't be moved
The people who specified this job clearly don't know what they're doing and it's been left to me to sort it out and get it done
I can only install cables in a certain area along the back of the top panel to avoid internal fittings but you can only get one arm in, at best it's fingertips on a couple of locknuts and it's not possible to hold a pair of stilsons on locknut and gland at the same time even with two people
It may be possible to undo the top panel chock it up to get hands on but with some cables already in I won't know until I try
plus ceiling height is very low with cables coming off a tray in front of the panel so the bend radius is tight
Due to access hammer and screwdriver isn't possible either
I've already installed a bunch of 20/ 25 and a 32 mm glands and had to cut serrations on one side of the locknut to be able to tighten them from the top side
I'm going to try and do the same for the larger glands
Just wondered if anyone had been in a similarly badly designed situation and tried anything which worked well?
The issue is the DB is a new modular Schneider panel with removable sides all busbars switchgear etc is at the front and the access is really limited it's bolted to the floor and has large singles already installed in the top for the supply and therefore can't be moved
The people who specified this job clearly don't know what they're doing and it's been left to me to sort it out and get it done
I can only install cables in a certain area along the back of the top panel to avoid internal fittings but you can only get one arm in, at best it's fingertips on a couple of locknuts and it's not possible to hold a pair of stilsons on locknut and gland at the same time even with two people
It may be possible to undo the top panel chock it up to get hands on but with some cables already in I won't know until I try
plus ceiling height is very low with cables coming off a tray in front of the panel so the bend radius is tight
Due to access hammer and screwdriver isn't possible either
I've already installed a bunch of 20/ 25 and a 32 mm glands and had to cut serrations on one side of the locknut to be able to tighten them from the top side
I'm going to try and do the same for the larger glands
Just wondered if anyone had been in a similarly badly designed situation and tried anything which worked well?