  1. Greengo1990
    Offline

    Greengo1990 EF Member

    Location:
    SCOTLAND
    hyrdoboil trips mcb? Element is 2.4kw ohms test was 23 Ohms and IR was 300 odd. Had disconnected element from thermostat and power did not trip but element seemed perfect
     
  2. PEG
    Offline

    PEG Trusted Advisor

    Location:
    Manchester
    Hi,what else is on the same circuit,and 300 odd what?

    Sometimes,it takes a few cycles or change of duration,to tempt a faulty element.
     
  3. Greengo1990
    Offline

    Greengo1990 EF Member

    Location:
    SCOTLAND
    That seems to be all on circuit. IR was 300Mohms when the customer had turned the water boiler on it tripped mcb straight away
     
  4. dmxtothemax
    Offline

    dmxtothemax Regular EF Member

    Location:
    Australia
    Business Name:
    David Haddock Electronic Repairs
    Elements can behave strangly sometimes !
    replace it anyway
     
  5. stevethesparks
    Offline

    stevethesparks Electrician's Arms

    Location:
    Northampton
    Whats the size and type of mcb?
     
    • Like Like x 1
  6. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Have you seen it trip? If it's repeatable try a toaster in that outlet and see what happens. If it trips too then perhaps N-E cable fault somewhere.
     
  7. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    What Steve said ^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^^
     
  8. anthonybragg
    Offline

    anthonybragg Electrician's Arms

    Location:
    NORTHAMPTON
    Business Name:
    CHARLTEC ELECTRICAL LTD
    The O.P. is saying MCB N-E fault doesn't usually trip a MCB unless incorrect info.
     
  9. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Oops ... can't imagine what I was thinking o_O
     