Recently there was a post regarding separate cpc sizes, Consider a circuit of socket outlet that need to have high integrity earthing, wired in Twin and Earth as a Radial, where by you need to run the cpc in the form of a ring using the integral cpc of the Tand E and you need to run a further cpc to form the ring.
Easy enough you may say, now in PVC trunking or conduit it is a simple job, same size cpc as the main cpc, say 2.5mm2 as it's protected by mechanical protection ie the trunking or conduit.
What size would you use if you had wired the Radial, not in trunking or conduit but under the floor boards or in a ceiling void as an example, if my memory serves me well it use to be, if the extra cpc was enclosed in trunking or conduit it has Mechanical protection so the min size is 2., however if the cpc is not protected then the min size would be 4mm2, is this still the case or has it recently changed?
 
think you are correct with that last bit, but i'm not 100% certain. they change the regs more often than their underpants.
 
I think the minimum size of an unenclosed cpc being 4.0mm harks back to the days when solid 2.5mm single conductors were still commonly used. Being solid they would be more prone to breakage when used on exposed supplementary bonding. That could be total garbage but I seem to recall this from somewhere.
 
543.1.1 says 2.5mm minimum if mechanically protected and 4mm minimum if not. This is in copper or copper equivalent.
The reg also says that this minimum only applies if the cpc is not contained in an enclosure formed by a wiring system.
 
543.1.1 says 2.5mm minimum if mechanically protected and 4mm minimum if not. This is in copper or copper equivalent.
The reg also says that this minimum only applies if the cpc is not contained in an enclosure formed by a wiring system.
Thanks Andy, thought that was the case. So using another analogy, if you needed to run a cpc for a lighting circuit that had been wired in twin cable, you would run 4mm2?
 
Thanks Andy, thought that was the case. So using another analogy, if you needed to run a cpc for a lighting circuit that had been wired in twin cable, you would run 4mm2?

I recently ran a 4mm earth from a socket outlet to a metallic light fitting. The lighting was wired in twin.

As Andy said rewiring would be the best bet, but they had just decorated and newly fitted carpets so it wasn't an option.
 
I recently ran a 4mm earth from a socket outlet to a metallic light fitting. The lighting was wired in twin.

As Andy said rewiring would be the best bet, but they had just decorated and newly fitted carpets so it wasn't an option.
Nice one SC
 
what about the switch ?

The switch cable was T+E, so the metallic switch was properly earthed as well. Clearly some work had been undertaken but the main loop of the lighting circuit was twin.

They were advised that I wouldn't be able to continue with the other changes they wanted (more metallic switches, metallic light fittings) and that they should change to double insulated fittings and plastic switches, or go through the upheaval of lifting carpets and boards etc. to bring an earth to the rooms with metallic fittings.
 
The switch cable was T+E, so the metallic switch was properly earthed as well. Clearly some work had been undertaken but the main loop of the lighting circuit was twin.

They were advised that I wouldn't be able to continue with the other changes they wanted (more metallic switches, metallic light fittings) and that they should change to double insulated fittings and plastic switches, or go through the upheaval of lifting carpets and boards etc. to bring an earth to the rooms with metallic fittings.
Sorry SC how would the switch be earthed if the loop as you say was just a twin cable, or am I being hypercritical?
 
Sorry SC how would the switch be earthed if the loop as you say was just a twin cable, or am I being hypercritical?

Basically, the loop in/out were in twin, so the CPC on the switch wire was just floating until I dragged an earth to the fitting using 4mm from a nearby socket circuit. At that point I properly terminated the switch CPC and lamp body earth strapper to the newly supplied earth.

Not hypercritical, just I probably wasn't completely clear.
 
I've used 1.5mm single green/yellow stranded to earth a kitchen flourescent before, had no 4mm and better than no earth. And it was run in such a way as to avoid damage [under insulation]. And I can't find my tin hat either. :p
 
Basically, the loop in/out were in twin, so the CPC on the switch wire was just floating until I dragged an earth to the fitting using 4mm from a nearby socket circuit. At that point I properly terminated the switch CPC and lamp body earth strapper to the newly supplied earth.

Not hypercritical, just I probably wasn't completely clear.
Ahh all clear now, thanks SC
 
Basically, the loop in/out were in twin, so the CPC on the switch wire was just floating until I dragged an earth to the fitting using 4mm from a nearby socket circuit. At that point I properly terminated the switch CPC and lamp body earth strapper to the newly supplied earth.

Not hypercritical, just I probably wasn't completely clear.
Ahh all clear now, thanks SC, I just knew it wasn't what I was thinking it might be, just my mind is on over drive this evening. On a roll some may say.
 

Reply to Hypothetical question to ease my troubled brow in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
812
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K
Hello, I am an enthusiast amateur undertaking wiring of two outbuilding under a building notice. I am soon to be subject to a first fix inspection...
Replies
5
Views
944
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock