Recently there was a post regarding separate cpc sizes, Consider a circuit of socket outlet that need to have high integrity earthing, wired in Twin and Earth as a Radial, where by you need to run the cpc in the form of a ring using the integral cpc of the Tand E and you need to run a further cpc to form the ring.
Easy enough you may say, now in PVC trunking or conduit it is a simple job, same size cpc as the main cpc, say 2.5mm2 as it's protected by mechanical protection ie the trunking or conduit.
What size would you use if you had wired the Radial, not in trunking or conduit but under the floor boards or in a ceiling void as an example, if my memory serves me well it use to be, if the extra cpc was enclosed in trunking or conduit it has Mechanical protection so the min size is 2., however if the cpc is not protected then the min size would be 4mm2, is this still the case or has it recently changed?
Easy enough you may say, now in PVC trunking or conduit it is a simple job, same size cpc as the main cpc, say 2.5mm2 as it's protected by mechanical protection ie the trunking or conduit.
What size would you use if you had wired the Radial, not in trunking or conduit but under the floor boards or in a ceiling void as an example, if my memory serves me well it use to be, if the extra cpc was enclosed in trunking or conduit it has Mechanical protection so the min size is 2., however if the cpc is not protected then the min size would be 4mm2, is this still the case or has it recently changed?