electricshock

1. What do I put in the cpc size on the test schedule if the steel trunking and conduit is used as cpc?

2. same as above but for swa strands used as cpc?

3. how do I do zs at a 3 phase circuit with no neutral. My meter usually needs neutral to get zs measurment? (Unitest Telaris 0100 plus)
 
1. What do I put in the cpc size on the test schedule if the steel trunking and conduit is used as cpc?

2. same as above but for swa strands used as cpc?

3. how do I do zs at a 3 phase circuit with no neutral. My meter usually needs neutral to get zs measurment? (Unitest Telaris 0100 plus)


The NIC have a few accepted abbreviations for containment used as cpc..... 1. Trun, 2. Con, 3. SWA & 4. MICC.

Generally these should suffice regardless of what flavour of test form you use.

If you're sure your meter cant directly measure Zs, you can calculate if from Ze+(R1+R2).
 
I've never used the meter but can't you do a PSCC (Ri for that meter I think?) but connect L to Line and N to cpc?
The instrument shouldn't care that it is measuring Line to earth loop instead of the expected Line to neutral.

Like I say, I don't know your instrument so take this with a pinch of salt..........

RCDs will not like it of course if you have them!
 
Amtech does mine for me :):) drop down has trunking then a wee box asking size hey presto actual size in the cert
same for SWA,conduit altho not light gauge/heavy gauge conduit
 

Reply to I have a few questions concerning the EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
773
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock