I would agree, despite the initial appearance, it would likely be TNS.
However the arrangement seems odd, it would appear to be a split concentric cable, which would mean that this has been installed separately from the incoming supply as a supply cable would not be split concentric unless it is coming direct from a local transformer.
 
Thanks for advice guys.

Yeah I'm not great on supply side of things for times like this- also never actually worked with split concentric but was assuming that's what it was.

Obvs for a single phase usually quite easy to spot a TNS.

Also the installation is a commercial unit of steel construction-does anyone know the reason the supply authority picks the earthing system for supplies?......or does it just depend on the type of cable lying nearby?.........or even the weather that day....?
 
The dnos work under ESQCR regs so not to BS7671.
For routine connections a system/network planner will be the person who decides what the network can support with regard to the proposed installation. Above him/her is a network technician. Higher up the ladder is the Protection Specialist who is god-like within the organisation
 

Reply to Identifying Earthing System in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
739
Fitted a remote second consumer unit to a detached annex. The supply to it was from a tncs system. The new db has been changed to a tt system for...
Replies
1
Views
773
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
I have not had to do the wiring for a wet underfloor heating system before. I think I started a thread fairly recently and had some very good...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock