Hi All,
When I consult Table 41.3 for a Type C Breaker rated 16A I see s max Zs of 1.37 Ohms. However this value is defined for both a 0.4s AND 5s disconnection time. This is obviously correct so I am missing something. Fig 3A5 also shows the table 0.1s to 5s. Can anyone explain please?

Thanks

Jonel
 
Also take a look at manufacturers data, these often differ from the book as they have been designed to conform to both 60898 and 60947-2.
 
MCBs have two methods of tripping.
One uses a bi-metallic strip, which heats up as current passes through it.
If the current X time is correct the MCB will trip.
The other method uses a coil and if the current is great enough, the MCB will trip instantaneously (deemed to be 0.1s, though in reality is probably less, somewhere between 0.01 and 0.08s, or half to four cycles).
It just happens that the current which would cause the bi-metallic strip to trip in 5s is the same which would cause instantaneous tripping.
Fig 3A5 gives the maximum Zs required to allow an MCB to trip within the prescribed time limits for all circuits in a TN installation 0.4s for final circuits and 5s for distribution circuits.
 

Reply to I'm confused about Type C Breaker Disconnection Times in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I work in the events industry which works under 7909. This assumes that someone qualified 7671 etc has tested the distor's and designed a system...
Replies
12
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
Running some calcs I'm confused about what Zs to use when calculating 5 second disconnection times. In circuits with 1.5mm2-4mm2 cable a fault...
Replies
18
Views
4K
Doing calcs on swa supply to building as sub main from main three phase squard D board for single phase supply off of TN-S supply. I used cable...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock