jeremy

-
Mentor
Arms
Reaction score
222
My 1653 has suddenly started giving inaccurate results when testing rcds. On a ramp test, it indicates that its giving 33mA and not tripping the RCD, but another tester the same RCD is tripping at 24mA, which is about normal for a 30mA. Fluke are quoting a fixed repair cost of £216 + VAT, to change the board. Test 4 less are not aptly named as they want £240 + vat as a fixed repair cost! The tester is 6 years old and this is the first problem I've ever had ( apart from a fair bit of operator error in the early days!). Has anyone any suggestions as to what this problem may be or how it can be rectified without a board change?
 
Take it in for cal, report erratic RCD trip results, and see what the outcome is, they may even quote to fix it, these boards can be repaired if you know where to go, I dont unfortunately.

Cheers.........Howard
 
Thanks Sir Kit. I rang test 4 less, who calibrated it in March, to get their take on the problem. On the subject of calibration, they said that they just measure what the equipment is testing and issue a certificate with the results, they don't actually adjust anything, apparently the same as all "Calibration" companies. If they can't adjust anything, why do we pay so much for calibration?
 
Thanks Sir Kit. I rang test 4 less, who calibrated it in March, to get their take on the problem. On the subject of calibration, they said that they just measure what the equipment is testing and issue a certificate with the results, they don't actually adjust anything, apparently the same as all "Calibration" companies. If they can't adjust anything, why do we pay so much for calibration?

Haha...this chestnut!

As an Inst Tech, Calibration means checking an instrument then adjusting it to bring its outputs within specification. All within the quoted cost.

I've no idea how much adjustment these MFTs etc have on them, but surely there must be some.
Test Meter may help on that question.
If the gear can't be calibrated without repair, then extra cost is fair enough.
 

Reply to Inaccurate RCD test results from my 1653 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K
Hi, My new leakage tester arrived so I wanted to try it out, I connected it to the Line and Neutral meter tails and got a total leakage with all...
Replies
0
Views
1K
E
Can anybody help with this one? Installation: TT system, (Ra 27 ohms), 3 phase & neutral incoming supply. A 4 pole 30mA RCD is at the head of...
Replies
9
Views
2K
Anyone had problems with these rcds? Control Gear Direct, 30mA, 63A 2 pole.. I recently bought two 10-way dual rcd boards from denmans...
Replies
5
Views
2K
S
Hello, I am a diyer doing my own board change shortly (paying a premium for the honour to BC) and have a problem either with my tester or...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock