Think i may be onto a loser here but is it possible to wire a simple one way switch and have some sort of indicator like a neon WITHOUT having a neutral? Its for the water pump to push hot water when required to kitchen tap (it's a long way from cylinder). There is already power at the pump, just need a switched live return.
I have a 3 core flex coming from the pump but the switch has to match the other fittings in kitchen and is metal fascia, hence needs a cpc! So my 3 wires are used up..
It may be possible to link a cpc from an adjacent skt but it's all newly plastered.. I know MK do a surround thing with a little led requiring no neutral but this is lit when OFF.
I assume neon grid modules need a neutral? I have a DP neon switch which was bought for it but obviously this needs a neutral.
Worst case is to just use an ordinary rocker switch with no indication but thought I'd ask.
Thanks..
 
Is there actually a UK reg forbidding this? I'd be interested to hear how it's worded.

The CPC is both functional and protective and often circuit elements in many appliances and light fittings such as noise suppressors, surge arrestors etc already use the CPC for their functionality. A neon indicator would be over a megaohm so the load current would be less than a quarter of a miliamp, this would be less than many suppression circuits might leak to earth.
 
Yes BS7671 states that a conductor identified as G/Y can only be used as a earthing conductor, not got the book to hand to state ref number though.

Functional conductors are identified as cream, although some RCBOs do come with a G/Y flying lead
 
What you could do is sense the flow of the alternating current of the motor when the pump is turned on by the switch instead of sensing the voltage applied to the motor. What you would need is a current transformer connected to a low voltage LED. A number of manufacturers make a ready made current transformer connected to an LED - all you would have to do is thread the load's line conductor through the current transformer's hole and drill a small hole in the switch plate to push the LED lamp through. If the magnetic field from one pass of the load line conductor through the CT is insufficient to light the LED then all you have to do is loop it though a second, third or fourth time - obviously there is a limit due to the CT's hole size and the diameter of the wire. The one I thought you might try is CR Magnetics CR2550-R:

http://www.crmagnetics.com/Assets/ProductPDFs/2550.pdf

which will light the LED at 0.75Amps AC for one pass through the 9mm hole. You could buy other colour LEDs.

They can be bought from:

CR Magnetics CR2550-R - https://octopart.com/cr2550-r-cr+magnetics-1186351
 
Yes BS7671 states that a conductor identified as G/Y can only be used as a earthing conductor, not got the book to hand to state ref number though.

Functional conductors are identified as cream, although some RCBOs do come with a G/Y flying lead
Change the colour from G/Y to cream.
 
The CPC is both functional and protective and often circuit elements in many appliances and light fittings such as noise suppressors, surge arrestors etc already use the CPC for their functionality. A neon indicator would be over a megaohm so the load current would be less than a quarter of a miliamp, this would be less than many suppression circuits might leak to earth.
Do you mean I cd wire a neon across s/L and cpc?
 
you could, but it's not recommended. marconi gave you the solution. in post #5
 
Can you not just pull a 4 core in with the old 3 core?
 
What you could do is sense the flow of the alternating current of the motor when the pump is turned on by the switch instead of sensing the voltage applied to the motor. What you would need is a current transformer connected to a low voltage LED. A number of manufacturers make a ready made current transformer connected to an LED - all you would have to do is thread the load's line conductor through the current transformer's hole and drill a small hole in the switch plate to push the LED lamp through. If the magnetic field from one pass of the load line conductor through the CT is insufficient to light the LED then all you have to do is loop it though a second, third or fourth time - obviously there is a limit due to the CT's hole size and the diameter of the wire. The one I thought you might try is CR Magnetics CR2550-R:

http://www.crmagnetics.com/Assets/ProductPDFs/2550.pdf

which will light the LED at 0.75Amps AC for one pass through the 9mm hole. You could buy other colour LEDs.

They can be bought from:

CR Magnetics CR2550-R - https://octopart.com/cr2550-r-cr+magnetics-1186351
That looks interesting Marconi, i shall try that. Many thanks..
 
Is there actually a UK reg forbidding this? I'd be interested to hear how it's worded.

The CPC is both functional and protective and often circuit elements in many appliances and light fittings such as noise suppressors, surge arrestors etc already use the CPC for their functionality. A neon indicator would be over a megaohm so the load current would be less than a quarter of a miliamp, this would be less than many suppression circuits might leak to earth.
I shall try that too, just to see! oh this is fun,...
 
Do you mean I cd wire a neon across s/L and cpc?
Yes, I was suggesting the neon between the switched live and the CPC. Electrically speaking I wouldn't really see a problem with such a small current flow and many appliances and electonic power supplies already regularly have components wired between the current carrying conductors of the supply and the CPC which introduce small leakage currents into the circuit..... I know it's not ideal and can even understand it being classed as bad prictice, the only thing I'm not sure about is whether the UK regs explicitly take it off the table as an option.
 
You can over sleeve green/yellow with another colour and use it differently in a multi core, except for a single cable.
The problem with t&e is the lack of insulation in the cpc. You would need insulation to mains voltage to use it for anything else.
Also even if the fitting doesn't need a cpc, you still need to provide one to every termination, so you'd still need one from somewhere.
 
Re used the cpc to power a very small load
, the only thing I'm not sure about is whether the UK regs explicitly take it off the table as an option.
Depends if you are using it as a combined neutral and earth, which is forbidden, or just for filtering.
I'd say technically the latter as you are connecting a load, but I'd not be overly concerned re the current.
 
I like Marconi's solution but wanted to add something about running a neon to earth. As per Marvo, there are filtering components in electronic devices connected from L to CPC, which are legitimate and necessary to combat radio interference. However they are required to meet certain constructional standards which you neon-with-current-limiting-resistor indicator lamp may not meet because it was not specced to run to earth.

If I had to do this, I would use a class Y capacitor as an additional current-limiting measure - these are permitted between L & CPC and also L and exposed metal of class II equipment, as they are self-healing and unlikely to fail short-circuit. FWIW If the indicator current is less than 0.25mA then even in the event of CPC failure, the current available to the touch is below the prescribed limit for class II equipment. But whatever is limiting the current must have proven durability and integrity, just like cable insulation.
 
What you could do is sense the flow of the alternating current of the motor when the pump is turned on by the switch instead of sensing the voltage applied to the motor. What you would need is a current transformer connected to a low voltage LED. A number of manufacturers make a ready made current transformer connected to an LED - all you would have to do is thread the load's line conductor through the current transformer's hole and drill a small hole in the switch plate to push the LED lamp through. If the magnetic field from one pass of the load line conductor through the CT is insufficient to light the LED then all you have to do is loop it though a second, third or fourth time - obviously there is a limit due to the CT's hole size and the diameter of the wire. The one I thought you might try is CR Magnetics CR2550-R:

http://www.crmagnetics.com/Assets/ProductPDFs/2550.pdf

which will light the LED at 0.75Amps AC for one pass through the 9mm hole. You could buy other colour LEDs.

They can be bought from:

CR Magnetics CR2550-R - https://octopart.com/cr2550-r-cr+magnetics-1186351


I have a similar situation whereby I need to light an indicator lamp when the outside lights are left on. Problem is, the outside lights comprise of 2 x 5w GU10's. I assume this means passing the wire through the hole around 18 times, is that correct, and doable with a 1mm cable?
 

Reply to Indicator switch with no neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one, I want to use an ip rated light switch with a neon indicator to manually ovveride a PIR detector controlling an e27 LED...
Replies
1
Views
1K
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
827
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
418
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock