I am just heading out the door but you are right that more turns will be required for the lower load current of your application. To light the LED requires 0.75 AmpTurns of alternating magnetic flux. As long as the product of load current multiplied by number of turns equals 0.75Aturns then the LED will illuminate.
 
[I said:
"Colin33, post: 1410887, member: 18528"]I have a similar situation whereby I need to light an indicator lamp when the outside lights are left on. Problem is, the outside lights comprise of 2 x 5w GU10's. I assume this means passing the wire through the hole around 18 times, is that correct, and doable with a 1mm cable?[/I]

The CT's hole is 9mm diameter. The diameter figure I turn up for solid single core insulated 1mm2 is in the range 2.1 to 2.5mm. I reckon this will pass through at most 12-13 times. So, you you will have to use a lower csa flex - say 0.5 mm2- and protect it with a 1 A fuse and mark up this maximum fuse size - see:

1 Amp Plug Fuse - BS1362 - https://www.tlc-direct.co.uk/Products/TLF1.html

http://www.batt.co.uk/upload/files/4f3a_1231500485.pdf

If it was me, I'd see if 12 turns of 1 mm2 provided sufficient LED illumination and if not then use the 0.5mm2 flex and 1A fuse method.

Sorry for the delay in answering this last part of your post.
 
Last edited:
The CT's hole is 9mm diameter. The diameter figure I turn up for solid single core insulated 1mm2 is in the range 2.1 to 2.5mm. I reckon this will pass through at most 12-13 times. So, you you will have to use a lower csa flex - say 0.5 mm2- and protect it with a 1 A fuse and mark up this maximum fuse size - see:

1 Amp Plug Fuse - BS1362 - https://www.tlc-direct.co.uk/Products/TLF1.html

http://www.batt.co.uk/upload/files/4f3a_1231500485.pdf

If it was me, I'd see if 12 turns of 1 mm2 provided sufficient LED illumination and if not then use the 0.5mm2 flex and 1A fuse method.

Sorry for the delay in answering this last part of your post.

Thanks, I'll give this a go. I was hoping to get this LED into the MK grid module ( Which I'd bought to do the job before realising the lack of neutral) but I think that may prove impossible. I'm wondering how neatly the led can be installed into part of the switch backplate, has anyone else done this before?
 
Colin33 - did you have a successful conclusion to this problem please?

(Sorry to nag because you are no doubt busy but the EF love to know the outcome of threads after advice is offered otherwise it is all theory - and we are practical people who want to know what works or not).
 
Colin33 - did you have a successful conclusion to this problem please?

(Sorry to nag because you are no doubt busy but the EF love to know the outcome of threads after advice is offered otherwise it is all theory - and we are practical people who want to know what works or not).
Hi marconi, the client has been away so I've only recently been able to discuss the options with him. He has decided to leave things as they are for now, and hopes that the new brighter LED lamps I've put in his outside lights will make it more obvious if/when they are inadvertently left on. I'm rather disappointed because I was looking forward to experimenting with the current sensor!
I thank you and everyone else for the valuable input :)
 
Using a CPC for anything other than it’s intended use is not allowed on BS7671, you could look at using a LED wired in series in your circuit.
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny
 
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny
Every cable must have a cpc in it.

Over sleeving the g/y to use it as a live conductor removes it as a cpc, and that cable no longer has one.
It doesn’t matter how short that cable is.
 
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny

I think we're all well aware of the electrical properties of copper, regardless of the plastic covering it has. The issue is the identification, especially if the little bit of brown sleeving falls of at some point and someone assumes the grn/yellow wire is safe to touch.

The regs offer safe guidance in this case.
 
Every cable must have a cpc in it.

Over sleeving the g/y to use it as a live conductor removes it as a cpc, and that cable no longer has one.
It doesn’t matter how short that cable is.
Every final circuit must have a CPC, but it doesn't necessarily mean every cable has to.
 
Wrong - do people think that a piece of conductive material with green/yellow indicator sleeving works differently in any way than the other conductors?

It is a metal, the colour is only an indicator put there by the manufacturer for our convenience. If you then decide to place brown/blue/grey sleeving atop of the green/yellow, what possible difference does it make.

Earth core has not been bestowed with some magical curse, it is simple copper with a coloured cover. No decent Engineer would ever consider it any other way. The only consideration might be the reduced C.S.A. if it's PVC/PVC flat twin and skin.

In fact if you wanted to use g/y as line, blue as CPC and brown as neutral - with a good reason, there is nothing stopping you. The regs only state they should be clearly identified at access points and terminations. This could be the word LIVE, letter L, the word LINE, or a coloured section of sleeving.

AND... the regs are a guide, used to supplement/inform. We as qualified Engineers can deviate any way we choose, as long as it is safe, and justifiable.

Danny
Q1.53 Can a single-core cable having green-and-yellow insulation be used for any purpose other than a protective conductor?
No (with one specific exception). Single-core cables having green-and-yellow insulation must not be overmarked or otherwise identified, and must not be used for any purpose other than a protective conductor. The only exception is where such a cable is used as a PEN (combined protective and neutral) conductor, when blue markings must be provided at the terminations.
Regulation number(s):
  • 514.4.2
  • 514.4.3
 
Indeed it can, old thread but mk used to sell a neon indicator for light switches that connected across switch contacts. Haven't seen new ones for a long time but believe they are still available.
 

Reply to Indicator switch with no neutral? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Just a quick one, I want to use an ip rated light switch with a neon indicator to manually ovveride a PIR detector controlling an e27 LED...
Replies
1
Views
1K
Evening all, I had a quick Friday afternoon domestic job that has turned into a PITA and I'd appreciate your help. While adding some new lights...
Replies
10
Views
827
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
418
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
Good afternoon all, I have been asked to look at a problem with a bolted neutral but no one seems to know what exactly is the problem. SSE...
Replies
0
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock