Hi folks, could I have some advice please? I have 12 volts between the (presumably earthed?) metal cooker extractor hood and the earth of a wall socket. This rises to 20 volts when the fan and light are switched on. Yet when I connect a test lamp (no matter whether 3V or 12V or 240V) in parallel with the voltmeter, the voltage drops to zero, and the lamp remains completely unlit. I don't understand what's going on. Is this some sort of induced voltage on the cooker earth?
(a) Is this dangerous?
(b) What is causing it?
(c) How do I stop it?
Many thanks.
 
cmbcmb, I presume you are measuring the voltage with digital voltmeter, multimeter or multifunction tester.
If so, as you have found, as soon as you load this voltage it disappears. This what electricians call a 'Phantom Voltage' and is of no concern. The input impedance of modern test instruments is very high >10Mohms and therefore it requires less than a micro-ampere to produce a voltage reading. This means in practice that voltages that are induced on all conductive materials from adjacent circuits or other electro-magnetic sources.
Back in the day when analogue instruments were the norm, electricians favoured less sensitive versions of voltmeter because they were less responsive to the phantom voltages that are encountered regularly.
 
Last edited by a moderator:
yeah. but yourself a proper AVO Meter, analogue.
 
As stated above, it might not indicate a problem but I would certainly suggest for safety and peace of mind you test that the earth readings of the appliance and its circuit is within the specs of your local regulations. You need to do an impedance test, not a voltage test to be sure.
 
Have raided ark and found analogue multimeter, which says voltage is negligible, and when in parallel with digital meter drops the digital reading 20V to about 0.2V.
Continuity test says hood is not earthed, but label inside hood proclaims double insulation.
Thanks to telectrix, Marvo and R1CH-G for advice.
 

Reply to Induced earth voltage?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I've got a light with a ceiling rose in the kitchen. While rectifying some faults in the house I came across to the light and measure Neutral...
Replies
25
Views
5K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
737
Hi. Turned power off to change a socket front. Turned off at breaker not the RCD or mains. Checked that socket was dead got these readings Line to...
Replies
10
Views
3K
So I recently installed a new circuit to my loft as a dedicated burglar alarm and cctv circuit. When checking polarity and voltage with my test...
Replies
3
Views
2K
Came across a weird one today… Four single black stranded 12gaTHHN running through 1/2” conduit about 40’ to first outlet box and 70’ to the...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock