Simply you have induced voltage from some of the cables in the conduit. The current in these cables induces a voltage to in those cables which are not connected.

When you connect a DMM across the spare cables and ground the impedance of the DMM (10Mohm or more !) is so high that it sees this induced voltage.

My back to back (MSc qualified) spent hours offshore chasing this phantom voltage on an MCC before he sent me an email in the office and I gave him the reasons.

For this same reason the Dutch regulations (NEN) only allow testing for dead with a dipole tester. This tester has a button which when pressed increases the current flow through the tester to 100 mA.

This is why I prefer to use the old square D type coil based voltage tester over a DMM for proving dead.
 
As per Davesparks the voltage you read could be anywhere between zero and 230 depending on the potentials of the connected cables that the floating cable is lying next to. The actual voltage is pretty meaningless because it's not part of a recognisable circuit. Testers with different impedances will give you different numbers, typically it will be somewhere between zero and 115.

The current that you can draw from it will be microamps which is why even a high voltage is unimportant. You can charge a balloon up to thousands of volts by rubbing it against your jumper, but the charge stored is so low you won't get a useful measurement with any normal instrument. Like the balloon, the floating cable is just a conductor with some stray capacitance to things nearby.
 

Reply to Induced Voltage LED / Steel Trunking in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
547
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
729
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
I have undercabinet lights that are low voltage. They work xenon pucks just fine. I want to convert to low voltage LEDS. Supposedly these are...
Replies
8
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock