Discuss Inspect and test on lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Amp David

-
Mentor
Arms
Reaction score
904
When testing lighting circuits that contains multiple fittings connected to the circuit via plug in roses, are the readings for either R1R2 or R2 taken at the plug in rose or the fitting?

This question is aimed more at doing a periodic rather than at the initial verification stage. Personally I have always seen the plug in rose and flex connection to the fitting as an inspection, as its not fixed wiring, but may be wrong.

Thanks and hope for some help full contributions:helmet:
 
For a periodic inspection I would tend to take the easiest method of testing and if you can get to the connections at the rose then test at the rose, if it is easier at the pendant then test at the pendant (but as you say inspect the pendant in any case).
R2 is easy at the rose R1+R2 never easy on plastic fittings unless you use a switch earth.
 
Cheers Richard,

All the Klik roses are onto Besa boxes behind the suspended ceiling, so are a doddle to get to. My thinking was that if all tests OK at the rose, but who ever installed the light fittings balls up a connection in the fitting it self.
 
When testing lighting circuits that contains multiple fittings connected to the circuit via plug in roses, are the readings for either R1R2 or R2 taken at the plug in rose or the fitting?

This question is aimed more at doing a periodic rather than at the initial verification stage. Personally I have always seen the plug in rose and flex connection to the fitting as an inspection, as its not fixed wiring, but may be wrong.

Thanks and hope for some help full contributions:helmet:

That all makes sense, the plug in bit is as you say not strictly part of the fixed installation, so take your R1R2 at he rose. If you really want to test the plugged in part, then make an adaptor up for your meter and test it PAT fashion.

Cheers............Howard
 

Reply to Inspect and test on lighting circuits in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
428
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi Im an apprentice and just wanted to clarify domestic style wiring since i work industrial and don't deal with conventional wiring. in college...
Replies
1
Views
896
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
384
I live in Australia; you can use a socket tester to test the RCD for the power outlet circuit. Plug device to a 3-pin wall socket, set testing mA...
Replies
2
Views
879

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock