Discuss Inspection for converted camper in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Jay89

-
Arms
Reaction score
46
Hi,

A client has been asked to get an electrical inspection done on her camper that has been converted to a mobile bar, power to be via a generator.

Is anyone aware of a specific certificate for such things as a standard EICR would pretty much read N/A.

Thanks
 
The fixed installation in the mobile unit needs to comply with BS 7671 (including section 717 - Mobile or transportable units).

So if it's a low voltage mains installation, I'm not seeing why say a commercial EICR form would mostly be N/A. Sure there are some sections regarding supply, but the bulk of the EICR form will still apply.
 
Your client needs to have an EICR carried out as the electrical installation should be in compliance with BS7671 Section 717 as stated above. There is no such thing as a standard EICR because this Report covers a multitude of different installations.
 
Your client needs to have an EICR carried out as the electrical installation should be in compliance with BS7671 Section 717 as stated above. There is no such thing as a standard EICR because this Report covers a multitude of different installations.[/Q
.

Thanks westward, I was just wondering if there was a document more specific to this request
 

Reply to Inspection for converted camper in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've been asked by a client to 'mask off' the green LED charging indictor lamps within several emergency lights fitted within bedrooms on a...
Replies
11
Views
640
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
930
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
692
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
978

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock