Discuss Installation of WarmUp Loose Wire System - How To Fuse? in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

B

BobG

Hello folks, I have just finished installing a WarmUp DWS600 loose wire system in my bathroom.

A little more on it here, but essentially it's rated at 0.6kW / 2.6 amps.

Warmup DWS 600 Loose Wire Underfloor Heating Kit - http://www.directheatingsupplies.co.uk/warmup-dws-600-loose-wire-underfloor-heating-kit

How should it be fused? Would a switched fused spur with a 3 amp fuse be ok for this / any reason why I should not?

http://www.builderdepot.co.uk/bg-ne...ction-unit-with-neon-brushed-steel-fbs52.html
 
Yep, 3A is fine, but must protected by a 30mA rcd/RCBO if it's in a bathroom ( use an rcd fused spur if the circuit is not already rcd protected).
 
what he said ^^^^^.FCU on wall outside bathroom. stat. next to it.
 
Morning folks thanks for the replies. I will check on the fuse board at home if that particular circuit is protected by a 30mA RCD and report back. Fingers crossed it is!
 

Reply to Installation of WarmUp Loose Wire System - How To Fuse? in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi I hope someone can assist with this matter please. new extension on a bungalow and under floor heating has been installed in all rooms. new...
Replies
7
Views
2K
P
Hi Guys, I have three questions I would appreciate some help with if some kind sould could help me out. in a nutshell: I have a timed inline...
Replies
10
Views
4K
purple
P
A
Hi, I'm brand new to the forum, so please go easy on me! :-) I'm building a large extension, which includes a new en-suite bathroom. I...
Replies
3
Views
1K
Toneyz
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock