D

DuckyUC

Hi everyone

I try to buy/find a Instant tankless electric water heater in uk
as the flat I living in have no gas
and I want instant hot water supply

I contacted coop energy today and they able to do a upgrade of electric service to 100Amp, so now the question is what is the highest kw/amp water heater I could use?
ModelRecommended BreakerMaximum Amperage @240VRecommended Household Electric ServiceRecommended Minimum Wire Gauge
ECO 273 x 40 Amps DP112.5 Amps200 Amps3 x #8 AWG
ECO 243 x 40 Amps DP100.0 Amps200 Amps3 x #8 AWG
ECO 213 x 40 Amps DP87.5 Amps200 Amps3 x #8 AWG
ECO 182 x 40 Amps DP75.0 Amps150 Amps2 x #8 AWG
ECO 111 x 60 Amps DP57.0 Amps125 Amps1 x #6 AWG
ECO 81 x 40 Amps DP33.0 Amps100 Amps1 x #8 AWG
POU 61 x 30 Amps29.0 Amps100 Amps1 x #10 AWG
POU 3.51 x 30 Amps29.0 Amps100 Amps1 x #10 AWG

I know the ECO 8 is the open it recommend, but is it possible to fit ECO 21/18/11? as there will be a "save margin" for the Max amp use. I prefer the ECO 18 so even at the peak there still 25Amp left
 
Re: Best 14.4kw+ Single Phase Instant electric water heater exist in UK?

So how many kw needed to support 2 shower at the same time during the winter + kitchen washing machine/dish washer?
14.4kw/60Amp seem a lot but that is talking about the peak usage during the winter time. Most of the time only will be about 1/3-1/2 of the max load. If I get an under power heater 2 showers can't operate at the same that will lose the point of having 2 bathroom really. The water heater only cost about 1-2% value of the flat itself it is really no point to save money by get an under power water heater.
With hot water requirements you can apply a certain amount of diversity same as you can apply to electrical peak loads. Unless you have a massive family or a small guest house I wouldn't size the heater to the maximum possible hot water requirement. I have 5 bathrooms with 3 showers and 2 baths between them and we have a 150litre HWC immersion heater, we don't ever run short of water even though the same sized cylinder would be used in a single bathroomed flat for example. I think you've convinced yourself you need a 14.4kW heater but I think it would be worth getting some professional advice from a plumber before committing to the capital outlay and high installation costs of such a large system.

In answer to your last question you can get anyone who's competent to perform the installation. I personally would get a plumber to install the heater and the pipework and get an electrician to install the supply and isolator etc.
 
Re: Best 14.4kw+ Single Phase Instant electric water heater exist in UK?

With hot water requirements you can apply a certain amount of diversity same as you can apply to electrical peak loads. Unless you have a massive family or a small guest house I wouldn't size the heater to the maximum possible hot water requirement. I have 5 bathrooms with 3 showers and 2 baths between them and we have a 150litre HWC immersion heater, we don't ever run short of water even though the same sized cylinder would be used in a single bathroomed flat for example. I think you've convinced yourself you need a 14.4kW heater but I think it would be worth getting some professional advice from a plumber before committing to the capital outlay and high installation costs of such a large system.

In answer to your last question you can get anyone who's competent to perform the installation. I personally would get a plumber to install the heater and the pipework and get an electrician to install the supply and isolator etc.
Good idea, after I contacted the EHC 14.4kw manufacturer I notice that is not a instant electric water heater, it is design for central heater , now I plan to install the ZIP DEX12 11kw/48A model, I phoned several plumber and one of them did said what you said he need to get a quote from a electrician to know the whole cost of the project.
 

Reply to Instant tankless electric water heater? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock