Hi yesterday I sat my FICA test and during the insulation resistance test I’m not sure if I made a mistake

I measured it doing individual circuits I had the main switch at db on but forgot to turn on the mcbs

I measured between Line at MCB and earth and Neutral bar to MCB then neutral bar to earth but not sure if this is giving incorrect readings as i never turned on the MCBs for the circuits?
 
Measuring from the top of the MCB to the earth bar and also to the neutral cable (should not be in the neutral bar or you measure against all the other neutrals as well) and measuring from the neutral wire to the earth bar should be OK for individual circuits.

You would only have the MCBs on when doing a global test of the entire installation. Otherwise the MCBs being on (with main switch off) would link all the line conductors via the busbar.
 
Hi yesterday I sat my FICA test and during the insulation resistance test I’m not sure if I made a mistake

I measured it doing individual circuits I had the main switch at db on but forgot to turn on the mcbs

I measured between Line at MCB and earth and Neutral bar to MCB then neutral bar to earth but not sure if this is giving incorrect readings as i never turned on the MCBs for the circuits?
Did you pass? Apologies if you don’t find out on the day or if your heading back to do the Questions etc mine was that long ago so I can’t really remember. but it Seems to me like you forgot to do it like it says in the OSG? I made a boo boo on my trade test pinched a cable against the backbox in the remote motor control part of the circuit (that patricular wire wasn’t in circuit for IR tests because the contactor was in the open state)which went boom when the assessor tried to start the motor Still passed though, he said you’ve got 5 mins to find it and fix it or you Fail, opened it up and it became immediately apparent that’s what happened cut and remade the wire took extra care fitting the faceplate on and hey presto PASSED so don’t be too worried if you made a mistake you could still Pass
 
Last edited:
Basically it was the full installation I was to test but I done it through individual circuits so didn’t think I would need to remove the neutrals from the neutral bar but I never turned on any of the MCBs just the mainswitch was on but the power was isolated
 
I was getting readings greater that 500 mega ohms in fluke meter but when switching the 2 way switch it wasn’t changing and also the motor circuit was giving a reading without pressing the contractor but I had the motor control switched on
 

Reply to insulation resistance question FICA in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
650
During an insulation resistance test IR at an EICR I measured 0.0014 MegOhms from line to earth. When I disconnected the neutral from the neutral...
Replies
4
Views
1K
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock