DaveS

-
Reaction score
24
Hi all

Am doing 2394/95 at moment and trying to get procedure firmly stuck in head. Thing I'm getting a little bit confused with is with some of the vids/examples online some state to switch main switch on (obviously before supply connected) and others off. My thinking is that you might as well always leave off as you will only be testing from the load side terminal of this switch anyway? What would be the other reason for leaving on. The other thing not to sure about is why the need to link N and L terminals at board in some instances doesn't just testing outgoing live and earth bar give a complete reading. Sorry if missing something really obviously long day!
 
1.you r IR tests should always be done with the main switch locked off and the installation isolated.
2. you link L-N in the DB and test from LN - E if you have any equipment on the installation that may be damaged by the test. e.g. any IT gear, boiler PCBs, TVs etc.
 
Cheers lads just think I'm nit picking a bit really. Had checked them vids just think I need to watch how question worded and make sure I explain clearly also clarify when testing thru sensitive equipment and linking out
 

Reply to Insulation Resistance testing procedure in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock