- Reaction score
- 8,163
Hi all,
Well, this one is interesting and I have absolutely no idea what could be causing this.
Just added a PIR to a lighting circuit, very simple, disconnect the lamp and move the feed cables to feed a PIR and then onto the lamp itself. Nice straightforward.
Doing my testing for the minor works cert and the IR readings go something like this:-
2, 10, 100, 200, 450, 4.5, 350, 5.5, 400, 5, and so on.
The ramp up at the beginning I expect to see, but then flipping back and forth between lower values and higher values. All above the minimum 2Mohm, but a cyclic flip back and forth with steady timing.
I didn't test L-N, but the same thing happens on L+N-E, L-E and N-E and it happens at 250v and 500v.
Anyone got any suggestions as to what could cause this because as I say, I've got nothing?
Well, this one is interesting and I have absolutely no idea what could be causing this.
Just added a PIR to a lighting circuit, very simple, disconnect the lamp and move the feed cables to feed a PIR and then onto the lamp itself. Nice straightforward.
Doing my testing for the minor works cert and the IR readings go something like this:-
2, 10, 100, 200, 450, 4.5, 350, 5.5, 400, 5, and so on.
The ramp up at the beginning I expect to see, but then flipping back and forth between lower values and higher values. All above the minimum 2Mohm, but a cyclic flip back and forth with steady timing.
I didn't test L-N, but the same thing happens on L+N-E, L-E and N-E and it happens at 250v and 500v.
Anyone got any suggestions as to what could cause this because as I say, I've got nothing?