Discuss Intrinsically Safe blue cable in the Industrial Electricians' Talk area at ElectriciansForums.net
It is possibly the earth which is used to earth the IS equipment and is separated from the general electrical earth and is not there to carry fault current. Why do you ask because if those cables/circuits are incorrectly installed you could, depending on the environment asking be for serious trouble.Evening all, could someone enlighten me please as to what the function is of the small screen wire in an IS cable and where it should be terminated please. Bit short, but that's all really!!
Cheers.
It should be terminated EXACTLY as the drawing says.
No matter what anybody on here says or you think.
That's is the golden rule of the concept.
Reply to Intrinsically Safe blue cable in the Industrial Electricians' Talk area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.