Discuss Inverters running freezer in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
I have a large 240v freezer running off a 12 v solar battery bank via an inverter, I would like to have a small backup inverter for the freezer that will cut in if the main one fails, and save all my food. Any one tell me how to do this please ?
 
If the main inverter is alive 24/7, the backup inverter could be a type with inbuilt transfer switch (i.e. UPS functionality) that will detect the loss of the main inverter's output. Or you can get standalone transfer switches that would just switch the freezer from main to standby. But in both cases the standby inverter would also run 24/7. Better would be to add an inhibit relay that shuts down the standby inverter when the main one is alive, using its control input or switching the DC supply.

One thing to watch out for: The starting load of a freezer compressor is very high compared to its running load. It may only use say 150W for ten minutes an hour, but could require a 1500W inverter to reliably start it. Another thing you might want to build in is a delay on the transfer of say 5 minutes. If the main inverter fails while the compressor is running, it will transfer and try to restart against head pressure and usually stall. Normally this will trip the protector in the compressor which will try again after a few minutes. But if instead it trips the standby inverter to overload lockout, it might not then restart at all. This won't be needed if the standby inverter is large enough to sustain the compressor stall current until the protector trips.
 
What kind of failure are you expecting? Many modes of failure aren't going to be helped by a standby inverter such as battery deterioration, lack of PV output, MPPT or charger failure etc.
 

Reply to Inverters running freezer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hello, So I purchased a Novopal 2000w/4000w(Peak) Pure Sine Wave Inverter DC 12V to 110V/120V. I purchased this so I can hook it up directly to...
Replies
4
Views
539
Hi, agricultural off grid project, Victron inverter/charger, BYD LVS and Pramac GBW22P generator. The generator has a DSE4520 controller...
Replies
0
Views
200
Hello everyone, We had an electrician over, who fitted a 40a MCB in the house consumer unit to supply a new build garage. It's underground SWA...
Replies
14
Views
1K
I am a retired Electrician and started looking at Solar Power, (Black Magic to me), after much reading of "How To", I decided to build myself a...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock