Domestic CU change, TN-C-S. Lighting circuit has an Extractor Fan with Electronic timer installed. When performing IR test on the lighting, should i just test the whole lighting cct between L & N (connected together) and the CPC - I do not want to remove the cover of the extractor to disconnect at the terminals as i may damage the plastic housing. If i do the IR test in this way, should i make a note of it on the EIC - i am concerned that i should be testing between all conductors seperately when changing the CU and recording the results accordingly. Any advice please.
 
Last edited by a moderator:
test L and N (shorted together) to E, first at 250V, then at 500V. do not test across L /N. as you rightly say, damage could be caused.
 

Reply to IR Testing lighting cct with fixed bathroom extractor load in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
601
Hi everyone, I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking. I recently came across...
Replies
1
Views
744
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hello I have an old timed extractor fan in the bathroom which has stopped working. It has 3 wires which are black, brown and grey. I believe that...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock