Hi All,
Firstly I'll apologise for not trying to collate this with another thread, But thanks to my organisation skills I find myself short on time.
I'm currently at College and coming up to a assignment to do with testing etc. I understand pretty much all area's of testing, However theres a few things that keep popping up and there simple things that could make me fail my test. So could you clear the following up for me.

1) When Doing an individual (i.e. not global) IR test do the MCB's need to be on or off?
2) We have it drilled into us to disconnect RCBO's and every time i do testing I'm now worried that i arent disconnecting them properly, At the moment I just disconnect the L,N and cpc's from the rcbo's, Is that enough or do I need to do anything else?

Any other helpful advice always well appreciated
Thanks in advance
James
 
you are correct. fo IR testing, you are testing the circuit under test L-N, L-E,N-E. the MCB/RCBO should not be connected to the circuit under test.
 
Hi mate,

You are IR testing the cables only.

I am assuming single phase here.

Isolate, lock off, post notice, prove dead then,

Disconnect the circuit completely from the dist board, then IR on the cable ends, L-E, L-N, N-E. Job done.
I see no reason to leave it connected to the MCB, and i wouldn't teach anyone to do it like that either. There is no need or purpose in IR testing the breaker.

Three phase do the same with all three phases.

Cheers.........Howard
 
Thanks for the help guys, It does seem alot easier to disconnect the cables completely, I have always been tought both at work and college to test to the MCB, Hence my question. But I guess removing the cables removes any doubt.
Thanks for your help



Disconnect the circuit completely from the dist board, then IR on the cable ends, L-E, L-N, N-E. Job done.
I see no reason to leave it connected to the MCB, and i wouldn't teach anyone to do it like that either. There is no need or purpose in IR testing the breaker.

Cheers.........Howard
 

Reply to IR Testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
429
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
618
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
818
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
784
Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock