Discuss Is it OK to terminate switched fused spur with 13A socket? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
16
I am planning a new layout for our utility room and would appreciate some advice. We have three appliances (washer, dryer and freezer) that will sit under a worktop directly below the window. My intention is to feed this equipment via a row of three 13A fused spur switchplates located inside a tall larder unit to the right of the appliances.

Would there be any problem in terminating each of these switched fused spurs with an unswitched 13A socket instead of cutting off the moulded plugs currently fitted to the appliance power cords and hard wiring each cable to a flex outlet box?

Another issue is the risk of trapping the mains cord when one of these big and heavy machines is pulled out from under the worktop for servicing and then pushed back. There will only be a 23mm gap between each machine, so it will be impossible to see what is happening behind the appliances. The only solution I can think of is to pull the loose mains cord up and across the top of the machine before it is pushed back under the worktop. The loose cable would then be pushed back out of sight once the machine is in place.

Are there any better ways to minimise the risk of trapping the cable?
 
Welcome to the forum.
Having a plug behind an appliance would mean that the appliance would have to be removed to change a blown fuse, not a terrible thing since if there is a fault you would probably have to remove the appliance to repair it first, however it can be an inconvenience.
Also having two 13A fuses in series is redundant and you could just go for 20A DP switches instead of SFCUs, but this ensures that the fuse to blow will be the one in the plug top.
The cable run of running three independent cables in safe zones behind the sockets will be a nightmare of space so at least 35mm back boxes to allow space for the through cables.
With only 23mm behind the appliance you will have to hope they are slim plugs because that is close.
I pull appliance cords in the way you describe, but you can tie a string to them to keep them up and allow you to pull it back again when drawing out or tape/clip them to the back once the appliance is almost to the worktop.
 
Personally I cut the plugs off and wire the appliances in to 20A flex connection plates especially for built in appliances but prefer it for all appliances. It’s much simpler to replace the fuse above the worktop and as said above an awful lot of appliances won’t go fully back with a plug behind them. And building standards are much happier with this here now too but building standards seem different everywhere lol
 
Thanks to everyone for their rapid responses to my first post on this forum.

It's the gap between each of the three appliances that is 23mm. I will be using a standard 60cm deep worktop, so there should be adequate space behind the machines.

My primary concern was to make sure that I had not missed some obscure new regulation that forbade the use of a 13A socket downstream of an SFCU. Replies so far suggest that this is not a problem. However, I have not given up on the alternative solution of cutting off the appliance plugs and hard wiring to flex outlet boxes behind each machine. Which method is most common in the trade?

I guess it is a matter of the convenience of a plug connection versus the convenience of a readily-accessible fuse (with two fuses in series, sod's law determines that it would always be the more inaccessible fuse that will blow first).

The idea of taping or clipping most of the surplus cable to the back of the machine just before it disappears under the worktop seems a good way to avoid it being trapped under the appliance. As long as the 60cm of free cable is fixed fairly high up at both ends, then it should only drop down by 30cm as the machine is pushed back, which is not enough to reach the floor.
 
most common way is a 20A D/P switch ( neon optional) above worktop for isolation, feeding a single 13A socket below
That does have the advantage that if anyone carelessly put some strain on the power cord when pulling the machine out from under the worktop then it would probably just disconnect the plug (unlike a hard-wired connection).

From my own experience, appliance fuses very seldom fail, so perhaps having the fuse hidden behind the kit is not much of an issue.
 
If you are still 'planning' your new utility room, there is also the consideration of how these appliances are supplied; especially a separate washer & dryer, which potentially could have a load of 2.2kW each. This could put a disproportional load, if they are connected at the same point on a ring final circuit for example?

Why not consider buying a combined washer/dryer, alleviating the issue above, and freeing up space below the work top for an additional cupboard where sockets for just two appliances could be placed.
 
I am still very much in the planning stage, as I like to work things out on paper before picking up any tools, but one decision has already been made. We tend to avoid dual-purpose kit in favour of dedicated devices, so when our 17-year-old washing machine died a few weeks ago, we replaced it with a new washer and dryer (we never had a dryer before).

I was already planning to check out whether or not I need a new ring main to handle the additional electrical load, but thanks for the reminder.
 
.... an awful lot of appliances won’t go fully back with a plug behind them...
I've now checked more carefully behind each of the three appliances and found that the position of a 13A wall socket would have to be completely different for each machine to allow them all to be pushed back against the wall. You need a minimum of 30mm clearance to accommodate a plug and socket. Large areas behind each machine are much closer than that to the wall.

In the case of the freezer, the wall socket would have to be quite close to the floor, making it a little trickier to avoid trapping the cable when moving the machine.

I guess there must be ways to install a 13A socket that is set back 30mm into the wall, but it would probably take quite a bit of effort.
 
I've now checked more carefully behind each of the three appliances and found that the position of a 13A wall socket would have to be completely different for each machine to allow them all to be pushed back against the wall. You need a minimum of 30mm clearance to accommodate a plug and socket. Large areas behind each machine are much closer than that to the wall.

In the case of the freezer, the wall socket would have to be quite close to the floor, making it a little trickier to avoid trapping the cable when moving the machine.

I guess there must be ways to install a 13A socket that is set back 30mm into the wall, but it would probably take quite a bit of effort.
Can you not install the socket in a position that doesn't impede the FF or is the flex not long enough?
 
I've now checked more carefully behind each of the three appliances and found that the position of a 13A wall socket would have to be completely different for each machine to allow them all to be pushed back against the wall. You need a minimum of 30mm clearance to accommodate a plug and socket. Large areas behind each machine are much closer than that to the wall.

In the case of the freezer, the wall socket would have to be quite close to the floor, making it a little trickier to avoid trapping the cable when moving the machine.

I guess there must be ways to install a 13A socket that is set back 30mm into the wall, but it would probably take quite a bit of effort.

I do a lot of kitchen refurbishments, hardly ever locate the socket behind the appliance for problems you've encountered. Similarly, locating 3 appliance adjacent to each other will also present the problem of flex length of each appliance.

Can you not redesign your layout?
 
Our utility room is only long enough to take the row of 3 appliances with one storage cupboard on either side, so I don't really have any alternative layout options. There would be no cord length issues if the sockets are directly behind each machine.

I might give myself more flexibility on the location of the 13A sockets if I use the following recessed box I have just discovered:

Sync-box solves slim TV wall-mounting blues - Inside CI - http://www.insideci.co.uk/news/sync-box-solves-slim-tv-wall-mounting-blues.aspx
 
Our utility room is only long enough to take the row of 3 appliances with one storage cupboard on either side, so I don't really have any alternative layout options. There would be no cord length issues if the sockets are directly behind each machine.

I might give myself more flexibility on the location of the 13A sockets if I use the following recessed box I have just discovered:

Sync-box solves slim TV wall-mounting blues - Inside CI - http://www.insideci.co.uk/news/sync-box-solves-slim-tv-wall-mounting-blues.aspx

You could try contacting the service department for your new appliances. They will often supply replacement leads for damaged ones, and in some cases provide additional longer leads, that negates the problem of hidden plug top fuses behind kickboards etc.
 
You could try contacting the service department for your new appliances. They will often supply replacement leads for damaged ones, and in some cases provide additional longer leads, that negates the problem of hidden plug top fuses behind kickboards etc.
That's an interesting thought. The two new machines both have quite short mains cables, especially the washing machine.

With longer leads, I could consider installing all three sockets inside an adjacent tall larder unit. In that case, I guess I would just use switched sockets and forget about having DP isolation switches.
 
Our utility room is only long enough to take the row of 3 appliances with one storage cupboard on either side, so I don't really have any alternative layout options. There would be no cord length issues if the sockets are directly behind each machine.

I might give myself more flexibility on the location of the 13A sockets if I use the following recessed box I have just discovered:

Sync-box solves slim TV wall-mounting blues - Inside CI - http://www.insideci.co.uk/news/sync-box-solves-slim-tv-wall-mounting-blues.aspx

I've seen the Sync-box before, but not used it myself. The only issue with them is the back box required, which I believe is about 47mm? Just bear that in mind in your install. It still has the issue of fuse behind appliance. I would check with the manufacturer to see if they will supply a longer lead.
 

Reply to Is it OK to terminate switched fused spur with 13A socket? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
356
Hi So converting a 6mm cooker connection point into a 13a unswitched fuse spur with the load being a 2.5mm pre wired cable from a oven . is this...
Replies
2
Views
2K
Extremely newbie question here. I'm looking to remove a redundant electric fireplace heater - it's wired into a switched fused spur on the wall...
Replies
5
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
772
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock