Discuss Is RCBO required ? in the UK Electrical Forum area at ElectriciansForums.net

PAD66

-
Reaction score
15
Hi.
I have recently qualified and started out on my own, I have asked by a been by a mate who is a plumber to renew the cable to the light fitting and switch in a bathroom that he has stripped back to bare brick for modernisation. They also want a shaver point and extractor fitting. No RCD on CU which was replaced in 2009. Am I right in thinking I need to install a RCBO for the bathroom lighting circuit as it is not a like for like replacement with the additions. I want to get this right as I intend to use it as part of my NICEIC assessment.
Advice appreciated.
 
Absolutely yes, all circuits feeding into bathroom need to be RCD protected, you may get away with it for true like for likes, but in the case you describe, no question you need the RCD.
 
yes it will require rcd protection unless you want to go down the 50mm cable depth thing, so changing the breaker for an rcbo would be the most straightforward way of doing it.
 
yes it will require rcd protection unless you want to go down the 50mm cable depth thing, so changing the breaker for an rcbo would be the most straightforward way of doing it.

nothing to do with the 50mm rule. it's a bathroom. so as kingeri said, RCD essential.
 
Instructions for fan says requires a 3A fuse. Shows it on the live feed before everything. This to me seemed a bit odd as it would also be protecting the light and the shaver socket. Did think of putting it after but was not sure if I would have to protect the switched live as well as the permanent live.
 
Instructions for fan says requires a 3A fuse. Shows it on the live feed before everything. This to me seemed a bit odd as it would also be protecting the light and the shaver socket. Did think of putting it after but was not sure if I would have to protect the switched live as well as the permanent live.

Yes you need to put it to the initial feed before the light/fan don't use gu10's with 3a fused fans they like to take the fuse out when they blow

From my experience anyway
 

Reply to Is RCBO required ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
702
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
835
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock