Thanks all; I've asked the electrician to come back to rectify the issues I've found. He is a busy guy, and I suspect that what happened is that he was so busy that he got a newly qualified/apprentice to do the work, and didn't have time to check it himself. I've also found an additional issue - a 45 amp cooker circuit on a 16 amp type B MCB.
As you've suggested, I'm going to get an EICR done by an electrician qualified to do commercial fixed wire testing. I'm hoping this won't be too intrusive given carpets and floors are down, but safety has to come first.
Midwest, I'm somewhat familiar with electrical installations, but not familiar with British domestic standards and common practice. To be honest, I'm only discovering most of the story/issues myself piecemeal as I look around the place.
As you've suggested, I'm going to get an EICR done by an electrician qualified to do commercial fixed wire testing. I'm hoping this won't be too intrusive given carpets and floors are down, but safety has to come first.