Discuss Issuing and installation certificate in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
92
I had an emergency call out to replace a consumer unit, (used a fully 18th edition compliant board) when compiling the installation certificate your not allowed any limitations.

now i know the rest of the house does not need to conform to 18th edition standards but The house is a large house so asides from anything obviously non compliant highlighted in my testing am i expected to ensure 100% of the installation is con formative because i cant with cables being in floors wall and partitions, i also certainly wont be dropping every accessory.

Where do i stand on this?
 
You are not required to make sure the installation in the rest of house is compliant, if you were every board swap would be a rewire for me.

You are required to ensure that all connected and energised circuits are safe. Your testing and cert will demonstrate this.

I suggest you download and read through best practice guide 1, it will help clear a lot of issues up.
 
you need to get readings for each circuit and ensure they are all safe to energise and safe for continued use. they don't necessarily have to comply with current regs.
 
You can’t have limitations on the board

As in you can’t ommit rcd protection for example

The remainder of the house wiring is irrelevant so long as it’s safe for continued use

If it wasn’t safe you probably wouldn’t be changing the board in the first place
 

Reply to Issuing and installation certificate in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
710
We've recently had a house rewired. There was about 2 years between first fix and second fix due to the pandemic and as the house was being...
Replies
9
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
425
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Afternoon all, Current situation is - Adult learner (I'm 38 in a few weeks) I have my Level 2&3 (obtained last September) started learning at...
Replies
3
Views
811

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock