Posting a message to the forum will remove the above advertisement
  1. This site uses cookies. By continuing to use this site, you are agreeing to our use of cookies. Learn More.
  2. angel While you're here, would you mind checking out our Electrician's Insurance section to see if we could save you a few quid? - Specifically our Van Insurance Deals and Public Liability Insurance Deals. Thanks for supporting the forum! angel

    5% Discount from Electrical2Go.co.uk for ALL members! - Click Here

  3. Forum for Trainees.

    If you are a trainee and haven’t already applied to join our trainee forum then click HERE The trainee forum is a closed area of the forum where the Forum Mentors will freely share their vast experience within the industry. 

    Dismiss Notice

Discuss just a thought! in the Electrical Wiring, Theories and Regulations area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. sparky1ste
    Offline

    sparky1ste Guest

    if a socket outlet is rated at 13amps why do weputit on 32amps MCB
     
  2. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    because the 32A MCB is protecting the cable that feeds several sockets.
     
  3. malcolmsanford
    Offline

    malcolmsanford Electrician's Arms

    You just had to answer .....................


    More to the point why do you have a 100amp switch and a 60amp main fuse ,eh tell me that
     
    Last edited: Feb 26, 2012
  4. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    can't you tell i'm bored. and why do we have 10A light switches on 1 light when the whole circuit is on a 6A breaker.
     
  5. sparky1ste
    Offline

    sparky1ste Guest

    So the accesories have nothing to do with it as long as we protect the cable in question. i had a lighting circuit the other day on 16 amp (normally bells starts to ring)Ref Method E Checkrd RegsMCB ok someone validated my cert. told me that should of failed because the light switch was only rated at 10amps
     
  6. telectrix
    Offline

    telectrix Scouser and Proud of It Respected Member

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    well then, "someone" is wrong. the MCB rating is selected to protect the cable. the light switch rating is selected to handle the load of the device it switches.
     
  7. Paul.M
    Offline

    Paul.M Electrician's Arms

    Location:
    Lost in Space
    Was it protecting 2.5mm by any chance?
     
  8. i=p/u
    Offline

    i=p/u Electrician's Arms

    16A is max allowed on lighting ciruit so is ok providing ...............
     
  9. Paul.M
    Offline

    Paul.M Electrician's Arms

    Location:
    Lost in Space
    Fare point, 1.5mm method E is up to 22A. Because its in cable tray it could be a long run and increased csa for volt drop.
     