    Hello Everyone,
    Need some advise. My fuse meter switch tripped . Upon inspection I realized that it trips the 'wall sockets' part only as the ceiling lights work fine on their own. I removed all the plugs from the appliance and reset the fuse box but after a minute or so it trips the socket switch again.
    Any help would be gratefully received.
    Its a Hager 6 way consumer unit with 2 test switch.
    Thank you All for reading my post.
     
  2. Cid
    Offline

    Cid Active EF Member

    Location:
    London
    You got a potentially dangerous fault in your wiring. I don't think you have what it takes to work out what so I'd recommend getting an electrician.
     
    • Agree Agree x 2
  3. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    Just to add to the above. They will also have the relevant test equipment to test the circuit.
     
  4. snowhead
    Offline

    snowhead Respected Member

    Location:
    Mildlands
    And another add, just check again that everything is unlpugged, it's easy to miss something.
    There may also be things connected into Fused units like these;
    FCU.JPG
     
    • Like Like x 1
  5. Wilko
    Offline

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi - as per @snowhead@snowhead #4, check the immersion electric hot water element is switched off. The element does sometimes fail.
     
  6. Jayhum
    Offline

    Jayhum EF Member

    Location:
    Slough
    Thank you all .for your advise. I will get an electrician to come over.
     
  7. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Can you be more specific. Meters record the amount of electricity used, they do not have trip switches.

    Perhaps you mean something in your consumer unit (aka fuseboard?)
    Does this something have a test button on it?
     
  8. Spoon
    Offline

    Spoon Forum Mentor

    Location:
    Lancashire
    I'm guessing the OP has a dual rcd board and the circuit breaker for the sockets has tripped.

    OP: Post a picture of your consumer unit. (fuse meter, as you call it..)
     
  9. Jayhum
    Offline

    Jayhum EF Member

    Location:
    Slough
    Sorry I meant its dual rcd consumer unit Hager 6 way mcb.
     
  10. Jayhum
    Offline

    Jayhum EF Member

    Location:
    Slough
    I noticed. if the mcb for the wall sockets part is left to OFF and the other two mcb is ON ie wall and ceiling lights. then RCB is fine. However if I switch the wall socket mcb to ON then on some occasions the RCB trips for all three and on some only the wall socket mcb trips leaving the lights working. Hope it makes sense.
     
  11. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    And is it the RCD that is tripping?
     
  12. Jayhum
    Offline

    Jayhum EF Member

    Location:
    Slough
    Ooops . Yes RCD, however on some occasions just the 'socket mcb' trips.
     
  13. Jayhum
    Offline

    Jayhum EF Member

    Location:
    Slough
    tempFileForShare_2019-01-11-13-59-39.jpg
     
  14. Taylortwocities
    Offline

    Taylortwocities Electrician's Arms

    Location:
    Oxfordshire
    Hmm. Sounds like you have a big fault somewhere.
    Do you have any outside sockets or other electrical stuff that run from that circuit?
     
  15. Jayhum
    Offline

    Jayhum EF Member

    Location:
    Slough
    Only a porch ceiling light.
    Here is a pic with the RCD switch tripped. tempFileForShare_2019-01-11-14-09-45.jpg tempFileForShare_2019-01-11-14-09-45.jpg
     
Loading...