    Block of flats having gas meters installed all in one location (a fair distance from MET).
    Its OK to have one earth bond chaining them together as long as the earth is unbroken isn't it?
    Therefore allowing one length of neat conduit running around exterior.
     
  2. Pete999
    Offline

    Pete999 Trusted Advisor

    Top Poster Of Month

    Location:
    Northampton
    Business Name:
    None
    Seems you are correct
     
  3. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    Is there a switch room/mains room with the meters in?
     
    • Agree Agree x 1
  4. Doomed
    Offline

    Doomed Electrician's Arms

    Location:
    Dorset
    Mains room with the 3 phase incomer and MET, new gas meters external on another edge of the block of flats.
     
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    sod the meters. bond to within 600mm of the pipes entry into the building. it's only gas monkeys that want to bond to external meters.
     
    • Agree Agree x 2
  6. Leesparkykent
    Offline

    Leesparkykent You Rock Gmes Staff Member Trusted Advisor

    Location:
    Kent
    What size is the incomer? You might have a hell of job sizing a bonding conductor and it being suitable to loop across the gas services.
     