Discuss Kitchen 'Smoke' alarm? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

T

Timbo_1975

Refit in a 2-up-2-down cottage with added Utility adjoining kitchen. Have 1st fixed interconnects in utility and landing for mains s/alarms.

Customer asked what was the position on having a heat sensor also in the kitchen?

What are peoples thoughts?
 
Smokes can't go in kitchens because of false alarms etc. I'm sure heat alarms are only needed when kitchen is not seperated from other areas by a door
 
Check the building regs,the way i read it was that they dont want you to fit them in kitchens,only to fit them if there is no door in relation to the circulation area between the kitchen and ground floor and then upstairs landing/bedrooms,me personally i would encourage,kitchen,hall,landing.I have had to do housing association works and they were in every habitable room,5 smokes and heat in kitchen,cant,perhaps a bit over the top to the regs but for the sake of a few £££ what price can anyone put on a life.
 
I had a building inspector recommend it to a customer and when I spoke to him he said it wasn't a requirement but he thought it was a good idea. Can't disagree really.
 
If its a heat detector it shouldn't cause problems

yep,i think they are rated to go off at 85C,so false alarms quite unlikely,most probable place for a fire to start,if that goes off its not the missus burning your dinner,i always fit heats in kitchens,customer always agrees even when they have a door.
 
Hi Timbo, as far as i,m aware according to BS5839 - 6:2004 alarms are fitted on a risk assessment being carried out, but also states that if the property is new build or materially altered then a heat detector must be fitted in the kitchen if not separated from a hall by a door, but if it is an existing property being fitted with a fire alarm system then a heat detector must be fitted in the kitchen. i might be wrong ( sometimes am gulp lol). hope this helps

check out www.aico.co.uk or BS5839 - 6:2004 and the Regulatory Reform Order 2005 (RRO) which the fire brigade seem to quote chapter and verse lol
 

Reply to Kitchen 'Smoke' alarm? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
289
Hi all! This weekend we have an offer on 8 of our most popular Smoke, Heat & CO alarms from trusted brands! Don't wait too long as these offers...
Replies
0
Views
334
I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
1K
Evening all, Currently 1st fixing new extension however the existing cooker hood duct which was on outside wall will now be part of new utility...
Replies
2
Views
658
Does anyone know what the new rules for England are for the rented sector smoke alarms and carbon monoxide detectors? Can they be battery powered...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock