S

shazbutz

Reading the installation instructions it states that a resistance test and an insulation resistance test have to be completed. No problem with the resistance test across the line and neutral through the foils that produces a figure well within the calculated tolerances for the area of film laid down. How is the insulation test carried out as there is no earth and the line and neutral are effectively the elements within the foils? I just know there is a simple solution..........
 
That's the simple solution I reached but the instructions state "test after the flooring is laid" which is tad disconcerting as the heating foils has disappeared under said floor!
 
Follow the manufacturers instructions if they are not available on site then download them or contact tech this way you can give a good judgement as to whether its been installed correctly .. their a hundreds of systems out there be it variants of the same brand or indeed different brands altogether so we can't give an informed answer without knowing which one you have.

Sorry you answered partly as i posted... contact the manufacturer then and ask them if the foil is the earth you can't connect it up without ensuring the foil has a good earth to it and as its now buried i think this is possibly going to be an expensive issue to correct. Ill reiterate though the instructions should explain if the foil is the earth.
 
Apologies, I did not complete my "that's the simple solution....". I was going on to say that it couldn't be the earth as the laminated foil (with line and neutral connections only) is laid on to a 6mm thick sheet of foam insulation and is therefore does not have a connection with earth. I take the point about contacting the suppliers tech team and will do so. But I'm left wondering if the insulation test requirement is a generic statement that is more appropriate to the wire based systems that the same organisation also sell.
 
Id be very surprised if the set up has no earth consider a fault to the floor that may be wet anyone turning the tap on in their bare feet (no sarky comments about why someone has a tap on their foot pls :) ).

It may be the case its double insulated but again check with the manufacturer is the best solution here if you don't have the info at hand.
 
It's a Swedish outfit called EBECO and despite reading their installation instructions over and over again the only reference to anything linked to an earth is the requirement for the "installation to be protected by a 30mA earth fault relay. The only occasion the word earth is used. What I'm now wondering is if in Nordic world a 6mm insulation sheet under and a 20micron film over is classed as double insulation!
 
and a metal grid if element does not have integral earthing.
 
Cheers Telectrix. Looking forward to a chat with there tech team....
Not sure if this helps or not. but its all I could find on the subject. I have never heard or seen the one you describe and would be interested to hear the outcome.
















Earthing Grid





You are here: Home » FAQs » Heat Mat Glossary » Earthing Grid
An earthing grid is a metallic structure that must be installed above an unsuitably earthed heating system when it is used in a wet area such as a bathroom. The earthing grid is connected to an RCD and this ensures that the system is switched off if there is damage to the floor.
In bathrooms it is a legal requirement to place earthing grids above many systems if including carbon films, some heating ribbons and any normal heating cables if they are not fully earth protected. Earthing grids add to the cost and time of an installation and it is always preferable to use a system with a fully integrated earth rather than having to install a separate earthing grid.







Tel: 01444 247020
 
Last edited by a moderator:
The more I read the more that it is as simple as 753.411.3.2. Good job the floor is far from fully down and is floating. The natural progression on this question now - where do I get the 30mm grid. Just searched CEF and local independent wholesaler with no joy.
 
I am interested in this as I have never come across a system without an earth, and I find it hard to believe that anyone would choose a system that would require an earth grid purely on cost grounds.
 
It's a long story! The Swedish manufacturers, despite multiple emails from me requesting an answer from their technical and design team failed to respond at all. The UK team's answer was pretty much no earthing arrangements as long as not in a wet room and must be protected by a 30mA RCD. When I pushed the requirements stated in BS7671, the response was pretty much; " yeah we have had a few enquiries about that but an earthing grid is not required."
The system was not selected on cost but the most appropriate for the construction of the kitchen floor and layout. The grid went in but played hell with the previously established levels so there was much huffing and puffing from the builder. I remain surprised that there is no reference to earthing in promotional clips, installation instructions or in quite a long YouTube video of an installation. Lesson learned!
 

Reply to Laminated Foil Underfloor Heating in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth? If all other tests are ok, what are the...
Replies
8
Views
5K
Looking for a little advice and also hopefully some education :) Have recently bought a flat (for which warranty period has expired) which has...
Replies
0
Views
3K
Hi - I have a Warm-up underfloor heating system. And it's stopped working. I did a basic resistance check - and clearly there's a problem (shows...
Replies
12
Views
7K
Hi all, wondering if anyone can help me with a recent issue I've had with electric UFH in a small flat. Found that when the UFH starts, the RCD...
Replies
19
Views
16K
Hi Guys! I've worked with a few qualified-electricians recently and I'm shocked with the large-scale misconceptions regarding the proper...
Replies
26
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock