robo83

-
Reaction score
40
I attend a job today and can see the Main earth is via a tag to the SWA lead.

I called DNO and they informed me if the ze is within permitted Tn-s values (which it was 0.20 Ohm) then leave it in place. I requested a PME upgrade and they wasn't keen since this was in place.

Looking for some advice with this, is it permitted or do I convert to TT.

Lead sheath SWA as earth 20180831_091121 - EletriciansForums.net
 
I suspect if you were to show them a photo of that earth clamp on their lead sheath they may not be so quick to accept it is their earth facility
There again if they have said its Tns why argue the point
 
Looks like a typical tns install, the ze is well within highest limit so there is no need to change it at all. Maybe just upgrade the earth bar there to an enclosed esco
 
I attend a job today and can see the Main earth is via a tag to the SWA lead.

I called DNO and they informed me if the ze is within permitted Tn-s values (which it was 0.20 Ohm) then leave it in place. I requested a PME upgrade and they wasn't keen since this was in place.

Looking for some advice with this, is it permitted or do I convert to TT.

View attachment 44026
SWA Lead??
 
it's not SWA, it's PILS (orPILC for some). that'sacommon way of providing a TN-S earthing. the lead sheathed cable is buried direct and the lead sheath provides the earth. pity about the DIY BS951 clamp though.
 
Looks like a typical tns install, the ze is well within highest limit so there is no need to change it at all. Maybe just upgrade the earth bar there to an enclosed esco
Typical....with that earth clamp?
 
Yeah I wouldn't trust that type of clampon a lead sheath but I also wouldn't touch it either if the Ze is good. What size wire is it between the earth bar and the clamp?
 
Yeah I wouldn't trust that type of clampon a lead sheath but I also wouldn't touch it either if the Ze is good. What size wire is it between the earth bar and the clamp?
Bit of 7/036 by the looks of it, or 4 mm2 for the kids.
 
You could be right with your imperial size, it looks like solid green colour insulation so probably quite old. I was quietly wondering if it was sufficient CSA for the supply...?
 
Thanks for everyone's input.

Pete 999, duly noted. I am reading up on the history of PILS cable now, to further enhance my knowledge.

I am going to call the DNO back when at the job and see if I get another decision/PME upgrade. If Its the same I will note on cert explaining.
 

Reply to Lead sheath SWA as earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock