Hello, I recently encountered a problem with a washing machine.
The washing machine tripped the RCD during its operation .
I visited the place, uncovered the metallic parts of the washing
machine and I searched for the current leak.
I measured a leakage of 0,450 Megaoghn between on leg of the resistance and the earth point.
I used a standard multimeter.
The funny thing is that mow the washing machine does not trip the RCD even if I take 0,450 Megaohm between one leg and Earth.

The resistance is capable of hotting the water without tripping the RCD.
 
Thanks for your reply,but I suppose that the problem is with
the resistance.Since I read a continuity (0.450 Megaohm)between one leg and earth, I think this was the problem. However ,this leaking does not trip the RCD immediately. Maybe , if the resistance works for a little time,then the leaking current will trip the RCD.
 
Hello, I recently encountered a problem with a washing machine.
The washing machine tripped the RCD during its operation .
I visited the place, uncovered the metallic parts of the washing
machine and I searched for the current leak.
I measured a leakage of 0,450 Megaoghn between on leg of the resistance and the earth point.
I used a standard multimeter.
The funny thing is that mow the washing machine does not trip the RCD even if I take 0,450 Megaohm between one leg and Earth.

The resistance is capable of hotting the water without tripping the RCD.
When you say you have 0.450 Mohm leakage, not exactly sure what you mean, alo what type of Multi Function Tester are you using?
 
I think he's using a standard multimeter.

OP, you may be seeing confusing measurements on your multimeter due to filter components between live/neutral and earth.

A proper insulation resistance test (at 240V initially) may be worth doing.
 
0.45MΩ will not trip an RCD. 230/450000=0.5mA of leakage worst case if that resistance is all from the line voltage side. If it's distributed between line and neutral the current will be lower. But a simple measurement of resistance probably won't find the fault anyway.

A washing machine has loads that are switched on and off during the cycle, bits heating up and cooling down, moving and then stopping again. So it's quite likely that the fault isn't present all the time. E.g. a damaged motor wiring loom might only short out when spinning an unbalanced load, element might only leak when wet, etc.

More investigation needed.
 
I'd still take note of the earlier replies.
A photo of where you have the test clips applied may be useful though.
 

Reply to leaking resistance _0,450 Megaohm in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
677
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
Replies
25
Views
6K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock