Discuss Led dimming problem in the UK Electrical Forum area at ElectriciansForums.net

B

brizospark

Installed 8 x integrated 7w NVC dimmable downlights today. 2 gang switch, one dimmer, one switch. The dimmer operateds the lights and the switch operates the fan (no timer, as per request of customer switched separate).

When lights are on and fan on all is ok, however, when I switch off the fan, the lights go off for about a second before coming on again, sometimes happens when switching fan back on again as well. Definitely no problems with wiring etc, just a straightforward circuit all installed by myself no different from usual.

Any ideas what could be causing this?

Dimmer is a varilight LED dimmer
 
Hmm, maybe the switching of the fan is causing noise or a spike on the neutral causing the dimmer to drop output. Maybe try a 2-pole switch for the fan if your neutral is at the switch.

**Edit** as another cheap option you could also try fitting a couple of MOV's across the supply and tied to the CPC as well. Something with a Vc of 750V and Imax maybe 3.5kA.

untitled1.jpg
 
Thanks Marv, so you reckon if i use a DP switch and a MOVaccross supply at switch this would work? How would I insulate the MOV conductors?
 
Try one thing at a time. You might not need both and there again it's all guesswork so neither solution might work as well. They're cheap as chips so I'd use a couple of them paralleled together across the L+N and another couple in parallel across the N+E.

Occasionally we use MOV's in panels and we just use thin heatshrink on the legs to insulate them and then much larger heatshrink over the whole thing to completely cover it once it's connected. Not sure what would be your best method in a domestic environment, maybe one of the UK guys has some advice.
 
Looking on one of my local suppliers websites we pay 88 cents for a 6KA MOV with a 275 V clamping voltage which would be about 5 pence in UK money and that's buying them singularly. The MOV's would be my first option as it would be cheaper than the d/p switch and in my humble guess it would carry the better chance of success as well.
 
I would start out with an MOV across the motor L+N. MOV's to the CPC will make it impossible to do insulation tests on the circuit and might not be needed. An R-C snubber might have similar success. The problem seems fundamentally that the dimmer is too sensitive to the transient.
 
Agreed a new dimmer of a different make would probably sort it out if the customer doesn't mind spending the money. As per Lucien, if you fit MOV's at the switch it would be nice for future guys doing IR tests if you left a note in the CU.
 
Or even a dimmer from the same make as it could just be a faulty component in this one.

And unless the customer provided the materials then they shouldn't have to pay extra for it to work correctly. If the OP has installed equipment which doesn't work then it's his lookout to fix it,
 

Reply to Led dimming problem in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
656
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
180
I have a led panel that i want to dim. It is dimmable but without a dimmable driver. I have a dimmer module and a dimmer switch as shown in the...
Replies
0
Views
519
The G4 110V 3W dimmable bulbs I purchased work with a dimmer. I can brighten them and dim them, but when I turn the dimmer off, the LED bulbs...
Replies
2
Views
905

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock