Novice here. I am looking to install (a lot of powerful) LED lights in my kitchen and I want to understand the implications of putting PSUs in my lighting circuit.

I currently have 15 halolite tube lights (16W each). That's 240W @ 240V (so one amp of current, right ?)

I'm thinking about bright LED strips which are 21W per metre. About 10m should be plenty - 210W in total.

Seems quite similar. But the ampage of these 12V strips is 1.75A per metre ... so 17.5A in total ! Now I'm more than a little wary of putting "so much current" through a lighting circuit !

I'll split the installation into two halves - with a 120W PSU (or "LED driver") on each. Each PSU talks about "10 Amps 240v to 12V DC Transformer (120 Watts)".

So each puts out 10A @ 12V creating 120W of power ... but what does it draw from the input side ? Assuming no losses, it must need 120W from a 240V supply which would be 0.5A for each driver, yes ?

So is it safe to use two of these PSUs in my lighting circuit and will they only draw a total of 1A (which is only the same as two of the old 60W light bulbs) ?





Cheers

Graham
 
about right. the current @ 12V is 20 x that at 240V. that's why you need larger CSA cables on the 12V side of driver/transformer.
 
Your current draw will be on the 230v so yes same as two light bulbs as for drivers they have a limit of say 120w maybe use upto 80w on each and not use them at full load or under load.

as for your psu/ drivers they might have a max distance like in normal transformers
 
that's why you need larger CSA cables on the 12V side of driver/transformer.

So do I need to use special cable for the links from the PSU to dimmer unit and then to my splitter ? I was going to connect 3-4 strips to each PSU (in parallel) so each of those would only carry a max of 1.75A.
 
But he's looking to extend the 12v side... Which depends on transformers / driver used

Is there a rule of thumb as to how far I can run the wiring between the transformer and LED strip ?

i.e. is there a "at 12V you lose x Watts/Volts every y metres" kind of law ? I'll be using pretty normal twin-core mains cable.

I think I'll keep a REALLY short link between transformer and dimmer, then another short link to my splitter ... and then run multiple feeds to the LED strips (@ "only" 1.75A each). That way, the longer cable runs won't have the bigger currents in them.
 

Reply to LED Driver Question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
720
I have three Aurora Fluorescent linkable (linked) under cabinet 'strip' lights (c.21cm each) under the kitchen cabinets and over the sink area...
Replies
2
Views
279
Hi all, Great forum with lots of advice read and greatly received over the years! I have a question here that I am hopeful somebody here can...
Replies
16
Views
1K
I am currently looking to add 12v led cob strip lights to my mother's kitchen but confused what I need. There are currently mains wires under the...
Replies
2
Views
565
I have an old IKEA Norrsken 12v suspended ceiling tension wire system, which runs x7 20w MR16 bulbs, from a Min 4x20w/Max 10x20w transformer. Can...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock