Hi new on here I am an adult apprentice fitted 2 new led fittings in an old house connected them up and at first switched on and off ok but my cousin called me telling me they aren’t switching on any more.

I have went back and checked they are just constantly dim.

It is not dimmer switches just 1 gang 1 way switches
Have no idea what’s gone wrong
Help would be appreciated
Thanks
 
I have a couple of faulty/very dim LED fittings, both had poor or no neutral connections (factory worker had not stripped the insulation before fitting crimp).

If you are an apprentice get whoever you work with to come with you to guide you through the fault finding.
 
Have you got a voltage tester to hand?
Check you've got 230v at the point of connection.
Are these '230v' LED's (plug into a normal lampholder, GU10, or whatever) or are they ones with a driver? Check the voltage on the output of the driver.
Also check it is a driver, and not a transformer. Transformers that came with 12v halogens are no good for 12v LED

If you've got 230v at the point of connection, then you've got faulty fittings if all the terminations are done properly.
 
Philips SceneSwitch: Switch light settings without switching bulbs | Philips Lighting - http://applications.nam.lighting.philips.com/blog/index.php/2016/09/20/philips-sceneswitch-switch-light-settings-without-switching-bulbs/

Have you perhaps fitted a Philips sceneswitch LED lamp which has 3 brightness levels or something similar? We have one on our landing which is controlled by a one way switch. When first turned on it illuminates at one of 100%, 40% or 10% levels. When turned off for a while and then turned on again it illuminates at the level it was at when last turned off (say 40%). So, to sequence to another light level(10%) one has to turn it on(40%) and then turn it off-on quickly. And then off-on again to sequence to the next (100%)and then off-on to return back to the first light level(40%). Maybe this is what you have installed?
 
No the leds are like built into the light fitting I’m gonna take fittings down and test by connecting plug and plugging into a switched socket to ensure the fitting works the fact that there is two light fittings on the one circuit makes me think there may be perhaps a fault in the circuit
 
Please let us know how you get on.

Just a thought - perhaps swap the switch for a new one. The surge current of the new LED lamps and their driver may have been the final straw for the contacts of the current switch.
 
The main difference between drivers and transformers is that drivers can handle the lower power used by LED fittings, whereas transformers are robots in disguise.

What?

A transformer is a wire wound device that changes AC voltage or current by electromagnetic induction. They can handle low power (or zero power output) with no problems.

A driver is a device specially designed to "drive" LEDs usually constant DC current, though the term is often used for constant DC voltage.
 
I only said all that to squeeze a joke in.

There are situations where a transformer for halogen 12v lamps didn't work properly for 12v LED. I'm now thinking its when theres a dimmer in circuit.
 
So poor neutral it was then. Yours hiding in the circuit (well done for finding the -------) mine much easier as it was in the fittings. Sorted ! I'm guessing they worked dimly due to the amount of leakage to earth.
 
Out of interest, during your fault finding did you do Zs at the light fitting?

I would have thought that a poor or lacking neutral would have been obvious using the 3 cable connections.
 
When checking it with test lamps I must have been pushing neutral up with lamps and was making connection as in junction box it was a snapped single core in neutral so was making sometimes I assume that’s why they worked fine when I’d left and perhaps opening and closing of toilet door affected the connection in junction box which was situated just above the door in toilet ceiling
 

Reply to Led light fittings constantly dim in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
Replies
4
Views
992
I have a street light circuit on land I rent out. I need to replace 2 of the bulbs. 1 of them is an old Philips 55W SOX Plus, the other is a...
Replies
3
Views
500
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
653
Kitchen led lights have all of a sudden dimmed by about 30% no dimmer in the system. There are 2 switches for this set of lights. Regardless of...
Replies
2
Views
807
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
552

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock