Hi,

I have a lighting circuit which trips the RCD, I’ve got pared back so that if I take one brand new light fitting and wire it directly into the consumer unit with a brand new cable - and still the RCD trips. If I remove that wire from the consumer unit and put a 3 pin plug on it, and plug that 3 pin into the mains rings, one sockets ring works fine and the other trips out.

The lighting ring is a 6A MCB and the socket ring that also trips out is a 32A MCB, both on the same RCD; the socket ring that does not trip out is also 32A, but protected a separate RCD in the same CU.

The CU was brand new a few months ago (not fitted by me, it’s a properly certified installation) and came fully populated. Total current draw at the main fuse is around 2A so the MCBs are definitely not overloaded.

How is this possible? Dodgy RCD?

Thanks
John
 
Hi,

I have a lighting circuit which trips the RCD, I’ve got pared back so that if I take one brand new light fitting and wire it directly into the consumer unit with a brand new cable - and still the RCD trips. If I remove that wire from the consumer unit and put a 3 pin plug on it, and plug that 3 pin into the mains rings, one sockets ring works fine and the other trips out.

The lighting ring is a 6A MCB and the socket ring that also trips out is a 32A MCB, both on the same RCD; the socket ring that does not trip out is also 32A, but protected a separate RCD in the same CU.

The CU was brand new a few months ago (not fitted by me, it’s a properly certified installation) and came fully populated. Total current draw at the main fuse is around 2A so the MCBs are definitely not overloaded.

How is this possible? Dodgy RCD?

Thanks
John
Borrowed Neutral,
 
The CU was brand new a few months ago (not fitted by me, it’s a properly certified installation) and came fully populated.
If I remove that wire from the consumer unit and put a 3 pin plug on it, and plug that 3 pin into the mains rings, one sockets ring works fine and the other trips out
I take one brand new light fitting and wire it directly into the consumer unit with a brand new cable - and still the RCD trips.
and you have wired it your self ?either you have a borrowed Neutral or its been wired up wrong .
 
From the description of what you have tried I cant see how it could be a borrowed neutral. You need to do an RCD test on both RCDs and also an insulation resistance test on the light fitting, and potentially a leakage test on the side that trips. It does sound like a faulty fitting and potentially faulty RCD. But it could also be that the side that is tripping has a high background leakage and that fitting is just tipping it over the edge. Is it some kind of LED fitting?
 
Finally got a chance to look again at this on Friday - it was a borrowed neutral. Thanks for all the help! :thumbsup:
 

Reply to Light fitting trips one RCD, but not if connected to a different RCD in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
735
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
553
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock