Hi

Customer wants a new light fitting in their cellar with battery back up - i.e. it runs off 230v and has a battery inside it in the event of power failure. Its not required to be on all the time.

Had a look at maintained and non maintained - having a senior moment - would either of these do the job?

Thanks
 
HERE

8 WATT EMERGENCY BULKHEAD LIGHT: Bulkhead Lights

Not a bad price.... and you don't have to stick the "running man" labels on if you don't want.

These ones (if they're the same as Denmans, which being Denmans internet branch they should be)

You can operate in Maintained / Non Maintained and also like the OP wanted switch between the two. So you can turn the light off, but in a "power loss" situation the light will ALWAYS come. If it's already on it'll stay on.
 
Last edited:
if you have it as maintained, it will always be ON. you need to feed a 3core to the light. L/N and S/L. switch will turn light on/off. if the power fails the battery will switch in. you need to wire it as non-maintained
 
It will always come on if there is a power loss whether the light is switched on or off. The internal battery is only designed to last 3 hours, (you may get more than this). If the power has been off for more than 3 hours, say in the middle of the night for instance, the battery may be flat and the light won't be working when everyone wakes up in the morning.
 
if you have it as maintained, it will always be ON. you need to feed a 3core to the light. L/N and S/L. switch will turn light on/off. if the power fails the battery will switch in. you need to wire it as non-maintained

So if I fit a "maintained" and connect the s/live to the unit only, it will be switched on and off by the switch. Silly question - without a permemant live how does it get charged? (or have I mistunderstood your answer?)
 
You need a permanent live whatever type you install, like you say to charge the battery.
With a maintained fitting you just add an extra switched live, using 3 core, which turns the light on and off.
 
You can also get Maintained units for standard fluorescent strips, and there are systems available that have a central battery system also to power them.
The latter may be a tad overkill for your installation though. I'd be more inclined, if the customer wants to be able to use them longer and on an irregular basis (i.e. doesn't want them just coming on and having no control), to install a LED lit, DC based system, from some lead acid batteries (but make sure they are ventilated properly) with a charging system.
 

Reply to Light for cellar with battery backup - suggestions please in the Australia area at ElectriciansForums.net

Similar Threads

Hi. Can someone let me know if this is right? I have a Led light which has emergency battery backup. Trying to figure out if what I have worked...
Replies
1
Views
2K
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
My view on life, in any field, is not to produce more but to consume less. Everybody told me this is a very eccentric weird mentality. Perhaps...
Replies
12
Views
2K
I don't normally get involved with domestic work but this job is for a family member so I cant Simpley say no. the house is a large property with...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock