D

daiplayer

Forgive me if im just being stupid...but the on site guide shows that a 1.5 mm cabe can carry a current of ...12a...or summat like that..cant remember now......

Why then do we protect lighting circuits with a 6a beaker ? ....or am just being dumb here..???:confused:
 
Its the installation methods and cable length that you use that determins the MCB size , you are incorrect when you say the on site guide shows 12 amp , table 4D5 BS 7671 , gives current carrying capacities and instalation methods ,and clipped direct a 1.5 mm cable will carry upto 20 amps , how ever you should never protect a 1.5 mm cable with that size breaker , voltage drop you are allowed 3% diversity so on long cable runs the voltage drop can be quite considerable , the other thing you look out for is the grouping factor when all the cables are grouped together ie on a cable tray in conduit , trunking etc , but the real crucial thing is insulation ,as i have mentioned clipped direct a 1.5mm cable can take 20 amps , stick it in trunking even a small piece then the current carrying capacity drops to 16.5 amps or cover it it no more than 100mm of insulation with one side touching plaster board then it drops again to 16 amps,enclose it in conduit in an insulated wall and it drops again to 14.5 amps ,cover it with more than 100 of insulation with one side touching plaster board and its then rated at 13 amps ,but if its surrounded by insulation even on a very short peice of the cable run then the cable rating will drop to 10 amps , hence the reason you tend to use 6 amp or 10 amp breakers and no higher , so in general terms its the maximum loading , cable drop ,installation methods , you can put socket outlets on 1.5mm as long as they are protected by a fused spur and as long as the installation methods are not 103 !one of the other items is the Zs ,although quite high 7.66 on a type B 60898 breaker the higher the current and type the lower the Zs readings so these should also be taken into account .1 hope that explains your question check out table 4D5 of the regs all revealed there
 
Last edited by a moderator:

Reply to lighting breaker sizes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
A really simple question. I'm sat here with my coffee and getting confused by it! 7.4kW EVCP. Would I fit a 32A or 40A RCBO? Not concerned with...
Replies
8
Views
6K
Hi A good friend of mine is having a large electrical installation carried out in his garden.Hes had 3 prices from various electrical contractors...
Replies
9
Views
2K
My customer currently has a shed at the bottom of his garden. The shed is approx 70m from the house as it is a huge garden. The shed has...
Replies
8
Views
3K
Hi guys, I'd appreciate the opportunity to pick your brains a bit, and make sure I'm on the right track, please. (Will also be talking to my...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock