If a 6a domestic lighting circuit had say at least 30 lights on it , including lots of 50w gu10 bulbs what code if any would you put on a eicr?
 
Depends
What regulation would you be citing on your observation ?
What exactly is the issue that requires a coded observation ?
 
If a 6a domestic lighting circuit had say at least 30 lights on it , including lots of 50w gu10 bulbs what code if any would you put on a eicr?
Lets have a bit more, what job? what exactly is the total load? how big is the existing cable? is all lights likely to be on at the same time at all?
 
Your max load if you have 30*50W GU10 is 6.25A so it will never trip on overload, it might trip on start up but as it is an EICR then it doesn't because it is in use, not a good design but never going to be a problem.
 
So if a circuit is really overloaded but has the correct mcb then you don't mention it on EICR ?

No you don't because it's not overloaded. The cable is adequate for the circuit and the OCPD is adequate for protection of the cable.

You should only be issuing a code to an observation on an EICR if it breaches a reg and you can reference that reg.
 
Yet again, I'm caused to call the competence of someone into question, when in fact by very requirement of quals such as 2391, anyone engaging in Inspection and Testing would be expected to have above average experience and knowledge.

Please, someone tell me that it's not just me thinking this, surely??!
 
Deleted.
 

Reply to Lighting circuits query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
373
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Hi all EICR today on a ground floor flat .. 1 issue .. At the consumer unit there was a 1mm core with its yellow (sleeved brown) in a 20A radial...
Replies
20
Views
2K
Hi guys. I had an inspection yesterday, where the lighting and sockets are in one circuit for each floor. There are 3A fused spurs for the...
Replies
11
Views
2K
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock