Maybe a bit of a silly question but im interested in what you would do......
2 gang switch situated in the hallway at the bottom of the stairs, 1x switch operates light in downstairs hallway off the downstairs lighting circuit and the other switch is the 2 way switch operating the upstairs landing light off the upstairs lighting circuit.
Would you join the 2 x cpc's together or leave the one from the 3-core disconnected so as not to join the two circuit cpc's together ?
 
Both CPC's should be connected to the box, individually sleeved.

All CPC's go back to one common point in the consumer unit, then to earth.
It's neutral conductors that you don't want joined (borrowed) as they may well be on different RCD's or RCBO's, its this that will give nuisance tripping.
 
Thanks for the replies chaps......
I have always connected both cpc's but have seen the 3-core cpc cut off from the upstairs circuit at the downstairs end....
 
^^^^^ Agreed, also this method provides a extra earth to the circuits should one of them get disconnected or break off.

The only thing is you would never know if you had a problem with a broken cpc on the other circuit, but at least you would be providing earth protection to that circuit through the switch cpc connection which is better than nothing. Then hopefully the earth fault would be picked up at some point.....
 

Reply to Lighting Circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
785
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
557
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
387
Hi I want to add a light to my attic. There is a single switch on the landing that I want to change to a double switch and then use it to still...
Replies
24
Views
1K
Hello, I'm replacing standard light switches in my hall and landing with touch switches (not smart, just touch on/off) like these from Amazon...
Replies
7
Views
569

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock